good day folks
out of interest, if anyone has filled in the “rated time delay” entry on an EIC for a 61008 type-s RCD main switch, what was the value (presuming the standard has a set value/range) used and where from ?
regards
Habs
good day folks
out of interest, if anyone has filled in the “rated time delay” entry on an EIC for a 61008 type-s RCD main switch, what was the value (presuming the standard has a set value/range) used and where from ?
regards
Habs
re: the table posted by @mapj -
is the ‘non-actuating’ value effectivel ythe max. allowed ‘delay’, so that for example, 130ms is the max delay that can be applied at Idn?
edit: to answer my own question, “no it isn't” as it appears to be the trip time range that is in BS7671.
re: the table posted by @mapj -
is the ‘non-actuating’ value effectivel ythe max. allowed ‘delay’, so that for example, 130ms is the max delay that can be applied at Idn?
edit: to answer my own question, “no it isn't” as it appears to be the trip time range that is in BS7671.