good day folks
out of interest, if anyone has filled in the “rated time delay” entry on an EIC for a 61008 type-s RCD main switch, what was the value (presuming the standard has a set value/range) used and where from ?
regards
Habs
The IET is carrying out some important updates between 17-30 April and all of our websites will be view only. For more information, read this Announcement
good day folks
out of interest, if anyone has filled in the “rated time delay” entry on an EIC for a 61008 type-s RCD main switch, what was the value (presuming the standard has a set value/range) used and where from ?
regards
Habs
I wonder if that box was intended for the likes of big boy's RCDs - earth leakage relays or add-on modules for MCCBs - that can have a definite (and likely constant) delay time.
S-types are just meant to be selective with instantaneous RCDs so often have a delay that varies with the residual current - so there is no one number you can sensibly write down.
I'd almost be tempted to write “S-type” and cross out the "ms".
- Andy.
I wonder if that box was intended for the likes of big boy's RCDs - earth leakage relays or add-on modules for MCCBs - that can have a definite (and likely constant) delay time.
S-types are just meant to be selective with instantaneous RCDs so often have a delay that varies with the residual current - so there is no one number you can sensibly write down.
I'd almost be tempted to write “S-type” and cross out the "ms".
- Andy.