good day folks
out of interest, if anyone has filled in the “rated time delay” entry on an EIC for a 61008 type-s RCD main switch, what was the value (presuming the standard has a set value/range) used and where from ?
regards
Habs
good day folks
out of interest, if anyone has filled in the “rated time delay” entry on an EIC for a 61008 type-s RCD main switch, what was the value (presuming the standard has a set value/range) used and where from ?
regards
Habs
AJJewsbury:
As long as it is slower than say 40mS
Perhaps because a 30mA RCD might take 150ms to trip at 100mA (according to table 3A) - it's only guaranteed to hit 40ms at 150mA.
- Andy.
I find that most of the R.C.D.s that I test trip off at about 22mS at 30mA trip test current.
Z.
AJJewsbury:
As long as it is slower than say 40mS
Perhaps because a 30mA RCD might take 150ms to trip at 100mA (according to table 3A) - it's only guaranteed to hit 40ms at 150mA.
- Andy.
I find that most of the R.C.D.s that I test trip off at about 22mS at 30mA trip test current.
Z.