This discussion is locked.
You cannot post a reply to this discussion. If you have a question start a new discussion

EIC "rated time delay" value for a 61008 type-s

good day folks

 

out of interest, if anyone has filled in the “rated time delay” entry on an EIC for a 61008 type-s RCD main switch,  what was the value  (presuming the standard has a set value/range)  used and where from ?

 

regards

Habs

 

Parents
  • AJJewsbury: 
     

    As long as it is slower than say 40mS

    Perhaps because a 30mA RCD might take 150ms to trip at 100mA (according to table 3A) - it's only guaranteed to hit 40ms at 150mA.

      - Andy.

    I find that most of the R.C.D.s that I test trip off at about 22mS at 30mA trip test current.

    Z.

Reply
  • AJJewsbury: 
     

    As long as it is slower than say 40mS

    Perhaps because a 30mA RCD might take 150ms to trip at 100mA (according to table 3A) - it's only guaranteed to hit 40ms at 150mA.

      - Andy.

    I find that most of the R.C.D.s that I test trip off at about 22mS at 30mA trip test current.

    Z.