good day folks
out of interest, if anyone has filled in the “rated time delay” entry on an EIC for a 61008 type-s RCD main switch, what was the value (presuming the standard has a set value/range) used and where from ?
regards
Habs
good day folks
out of interest, if anyone has filled in the “rated time delay” entry on an EIC for a 61008 type-s RCD main switch, what was the value (presuming the standard has a set value/range) used and where from ?
regards
Habs
missed the question.
The max non- actuation time for a given over current, is the longest pulse of that level of earth leakage over-current you might apply and be sure you can do so without the trip process ever starting - i.e. without ever passing the point of no return in de-latching. Note that you may be able to pass a larger current for a bit longer and even after the point of no return is reached may take quite a bit longer for the contacts to be actually open - hence the other figures.
So
a 100ma S type will not de-latch in 130msec at 100mA, but it may at any longer duration, and will always have de-latched and be open cct by 0.5 seconds at that fault current or higher
it will not de-latch in 60msec at 200mA, but it may at any longer duration, and will have both de-latched and be open cct within 200ms at that current or higher
it will not de-latch in 50msec at 500mA, but it may at any longer duration, and will definitely have both de-latched and be open cct within 150ms at that current or higher
the explanation under the table is poorly worded.
Mike.
missed the question.
The max non- actuation time for a given over current, is the longest pulse of that level of earth leakage over-current you might apply and be sure you can do so without the trip process ever starting - i.e. without ever passing the point of no return in de-latching. Note that you may be able to pass a larger current for a bit longer and even after the point of no return is reached may take quite a bit longer for the contacts to be actually open - hence the other figures.
So
a 100ma S type will not de-latch in 130msec at 100mA, but it may at any longer duration, and will always have de-latched and be open cct by 0.5 seconds at that fault current or higher
it will not de-latch in 60msec at 200mA, but it may at any longer duration, and will have both de-latched and be open cct within 200ms at that current or higher
it will not de-latch in 50msec at 500mA, but it may at any longer duration, and will definitely have both de-latched and be open cct within 150ms at that current or higher
the explanation under the table is poorly worded.
Mike.