Are 5amp junction boxes acceptable on a 6amp lighting circuit?
I personally wouldn’t use them as they are too small, but if they are already fitted are they acceptable?
I think there's a bit of history involved in your initial question, which dates back to the rewireable fuse days, 5A, 15A, 20A & 30A (metric values?!) When we harmonised round about 1980 the main IEC MCB equivalents were 6A, 16A and 32A (i.e. not metric!), so those values were introduced in the UK to harmonise.
The change from “round numbers” (5, 10, 30 etc) to what we have now (6, 16, 32 etc) is less to do with metrication and more to do with “preferred numbers”. It's an old idea dating back to a certain Charles Renard and ropes for French military balloons, but the underlying principle is now used very widely. Basically it's the idea of being able to serve a wide range of requirements with the minimum waste.
The idea is that every rating is within a certain fixed percentage of the previous one - so nothing need ever be over-sized by more than that amount. The choice of percentage varies but will be a compromise between having to manufacture and hold stock of lots of different values against the oversizing in the actual installation. Often the percentage is chosen so that the numbers fit exactly into a ‘decade’ - i.e. the sequence produced between 10 and 100 is the same as between 1 and 10 but multiplied by 10.
The value for electric stuff is usually around 58% - (actually the 5th root of 10) - dividing each decade into 5, which gives values (slightly rounded) like 1.0, 1.58, 2.5, 3.9, 6.3, 10, 15.8, 25, 39, 63, 100 and so on. Which (when rounded again slightly) gives us the familiar 1.0, 1.5, 2.5, 4, 6, 10, and 25mm2 cable sizes.
Using the 10th root of 10 (about 26%) gives ten values per decade: e.g. 1.0, 1.26, 1.58, 2, 2.5, 3.2, 3.9, 5, 6.3, 7.9, 10, 12.6, 15.8, 20, 25, 32, 39, 50, 63, 79, 100 and so on. From which (again with a bit more rounding) the familiar MCB/fuse sizes of 6A, 10A, 13A, 16A, 20A, 25A, 32A, 40A, 50A, 63A, 80A, 100A can be spotted.
- Andy.
Hello JDW.
I think there's a bit of history involved in your initial question, which dates back to the rewireable fuse days, 5A, 15A, 20A & 30A (metric values?!) When we harmonised round about 1980 the main IEC MCB equivalents were 6A, 16A and 32A (i.e. not metric!), so those values were introduced in the UK to harmonise. Close enough for no existing hardware changes to be necessary. Where found, an existing 5 amp junction box on a 6 amp MCB will be fine, all other things being equal. The small size makes cable sheathing enclosure a common failure with these - most guys installed 20 amp JBs for just that reason; the actual terminals themselves being similar in size.
Regards,
Colin Jenkins.
well once covered in site applied thermoplastic insulation, it may be argued to actually comply, at least until the tape peels off. Self amalgamating tape is better in that regard.
Mike.
(and there may be a few bits with my prints on too in strange places, but I'm not saying where. Mine is the one where the cables are knotted or cable tied to each other to give strain relief )
JDW:
I've seen quite a few that have been done like this, mainly on older installations (1990's and 00's) was it common practice then?
Alright Guv I'll confess. I done it. Honest I ‘ad to. Fitting a new light downstairs. Did I wanna go upstairs and move the double bed, roll back the carpet, cut a trap to fit a junction box, perhaps in a chip board floor that would creak a lot when walked on afterwards. I ain’t a chippy mate. Nah mate. I just used choc blocks to connect the new light. Taped all the chock blocks wiv good quality electrical insulation tape of the right colours, then stuffed the lot up into the ceiling void above the new light. Did I evva have any comebacks? Nah. All jobs were gooduns. No fires, no shocks no problems. Crickey mate, I woz doin' that when I was knee high to a dis board.
Z.
Still is common at the shallow end of the market, cheap kitchen re-fits and that sort of thing - it never was good practice, though as it will often work for years it all depends on how keen you are to safe a few quid but not quite meet the spirit of the regs.
Mike.