My house was rewired for me 20 years ago by an NICEIC registered firm of electricians. Concurrently a new BS7870PVC concentric cable was run down a pole on my land from overhead cables, then underground and finally up a hockey stick into a DNO head in a new external meter cabinet. Separately a 10mm cable from a new earth rod was run up an adjacent tube, to a MET in the same cabinet.  A conventional TT system, I presume. 

 

The (then) new internal CU (less than 2m from this cabinet) was fitted with 2 x 30ma RCDs between them feeding 14 circuits. One of these (protected by a 16a MCB) goes to a detached fuel store (copper tube connects a steel oil tank to the central heating boiler within the house). Another (also protected by a 16a MCB) goes to a detached now metal framed greenhouse and adjacent twin garage. Sub distribution boards in each outbuilding are fused down to 15a radials to every twin socket and to 5a for lighting. There is no EV charger yet. 

 

2.5mm 3core SWA cables connect the main CU to the sub distribution boards.

 

Does the armour in the SWA qualify as 10mm bonding ?

 

Should separate earth spikes be driven in, near the sub boards in each outbuilding?  If so, how should the (3 core) SWA best be terminated at origin (CU) and at each outbuilding?  

  • It's a rural supply with TT earth, what is wrong with it? The contents of the meter cabinet are an awful lot neater than most installations pictured in here. Any sign of woodworm in the pole?

  • round here, (rural hants) that would be a typical TT domestic take off. The lower line has the double line taps and is a PME ready neutral, or at least the double crimps are present, there may be very good reasons it cannot be PME. 

     

    If it ever fails it will be replaced by ABC.

    Not sure what is wrong with it sparkinghip - looks good to me.

    Mike.

     

  • I suspect the overheads may be TNS.

    If it was TN-S I'd expect 5 wires (if 3-phase) rather than 4. Single phase would be 3-wire of course. I suppose it could be split phase (2 phase, NE and PE) to make up 4 wires, but I've never seen that used for supplies to multiple premises (just individual farms/camp sites).

       - Andy.

  • Look at the picture of the overhead cables, the second wire up is thinner and doesn’t appear to have any direct connections to it to the concentric cables. bu there’s a supply taken off in singles to the bottom left and it has two insulated conductors and a bare cable off the second up, that’s the one that looks like TNS.

    da026873b5abbd8abd2a0177f6543a58-original-d2550b2f-8ea2-4e97-9f72-07115b8a6ad0.jpg

     

  • mapj1: 
     

    round here, (rural hants) that would be a typical TT domestic take off. The lower line has the double line taps and is a PME ready neutral, or at least the double crimps are present, there may be very good reasons it cannot be PME. 

     

    If it ever fails it will be replaced by ABC.

    Not sure what is wrong with it sparkinghip - looks good to me.

    Mike.

     

     

    It appears that the neutral connection is double tapped, but I would not want a TN-C-S supply off it and I would prefer the TT to using the overhead TNS if that’s what it is.

  • There could even be a switched live for street lighting, maybe unlikely but possible.

  • Back to the original post.

    You describe a fourteen way consumer unit with two 30 mA RCDs, this should have a higher rated upfront RCD to protect internal wiring and the busbars, if the consumer unit has a metal enclosure it definitely should have an upfront RCD.

  • Look at the picture of the overhead cables, the second wire up is thinner and doesn’t appear to have any direct connections to it to the concentric cables. bu there’s a supply taken off in singles to the bottom left and it has two insulated conductors and a bare cable off the second up, that’s the one that looks like TNS.

    Yup saw that - I couldn't make out how the top & middle were connected, but the bottom wire looked to be connected to top of the main distribution - so my guess was that it's feeding a 2-phase customer (common enough, one phase for normal, the other for night storage heaters) - but unusually with N in the middle (possibly the 2nd phase got added at the bottom at a later date).

    As the main line (left & right) appears to be just 4-wires, it's can't be 3-phase TN-S no matter how individual customers are connected.

       - Andy.

  • Sparkingchip: 
     

    Back to the original post.

    You describe a fourteen way consumer unit with two 30 mA RCDs, this should have a higher rated upfront RCD to protect internal wiring and the busbars, if the consumer unit has a metal enclosure it definitely should have an upfront RCD.

    In an insulated enclosure outside the metal consumer unit?

    Z.

  • In an insulated enclosure outside the metal consumer unit?

    Or could be the incomer in the steel CU provided the incoming connections were protected by double or reinforced insulation or equivalent (An insulating stuffing gland through the steel and the sheath left on the tails right up to the RCD might suffice).