5.2.8.5 Toilet facilities and changing rooms

For such a small paragraph in BS5266, I fend many questions with respect to when you must provide emergency lighting and when it should be supported with emergency lighting calculations.

I assume I am not alone in this, so I thought I would share my interpretation of the requirements. I could not find any information on when you would consider a multi-closet facility to have borrowed light, the assumption at the end is unfounded and my interpretation only. Comments appreciated.

[post comment] The original intend of this post was to find if this table helped simplify the process of determining the requirements for emergency lighting in bathrooms etc. The intent was not to discuss the design process, nor the question of what borrowed light is, or any other standard. 

Unfortunately, I am unable to delete the topic or close it.

Applicable for:    
Toilets    
Bathroom    
Showers    
Changing Rooms    
     
Use of SpaceProvision of Borrowed LightArea of SpaceEmergency
Lighting
Required
Calculation
Required
For Use by Disabled PersonsAll8m2 or lessYESNO
For Use by Disabled PersonsAllAbove 8m2YESYES
Single Closet FacilitiesWith Borrowed Light8m2 or lessNO-
Single Closet FacilitiesWithout Borrowed Light8m2 or lessNO-
Single Closet FacilitiesWith Borrowed LightAbove 8m2YESYES
Single Closet FacilitiesWithout Borrowed LightAbove 8m2YESYES
Multiple Closet FacilitiesWith Borrowed Light8m2 or lessNO 
Multiple Closet FacilitiesWithout Borrowed Light8m2 or lessYESNO
Multiple Closet FacilitiesWith Borrowed LightAbove 8m2YESYES
Multiple Closet FacilitiesWithout Borrowed LightAbove 8m2YESYES
Hotel Bathroom/EnsuitsWith Borrowed Light8m2 or lessNO-
Hotel Bathroom/EnsuitsWithout Borrowed Light8m2 or lessNO-
Hotel Bathroom/EnsuitsWith Borrowed LightAbove 8m2YESYES
Hotel Bathroom/EnsuitsWithout Borrowed LightAbove 8m2YESYES
     
Note: closet, wall and doors must allow borrowed light. Using standard partition sizes and typical minimum ceiling height this would include 300mm above, and 100mm below. Where closet cannot be provided with borrowed light then emergency lighting per closet should be provided.
Parents
  • mapj1: 
     

    oddly this very morning as I went to my local screw fix to pick up a box of ten hacksaw blades among some other stuff, and was given a large box.   I got to the car and as I loaded up then thought about it, and looked Inside, to see ten smaller boxes, each one of those holding ten blades.

    They were rather embarrassed when I went straight back in to return the 90 blades I had not ordered or paid for.  

    Computer said part XX, label on the big box said XX too. Application of original thought or common sense, not a lot.

    Mike.

    I must phone my broker, Kingfisher, sell, sell, sell. Kingfisher Group used to own that ubiquitous chain found on every U.K. high street, Woolworths.

     

    Z.

Reply
  • mapj1: 
     

    oddly this very morning as I went to my local screw fix to pick up a box of ten hacksaw blades among some other stuff, and was given a large box.   I got to the car and as I loaded up then thought about it, and looked Inside, to see ten smaller boxes, each one of those holding ten blades.

    They were rather embarrassed when I went straight back in to return the 90 blades I had not ordered or paid for.  

    Computer said part XX, label on the big box said XX too. Application of original thought or common sense, not a lot.

    Mike.

    I must phone my broker, Kingfisher, sell, sell, sell. Kingfisher Group used to own that ubiquitous chain found on every U.K. high street, Woolworths.

     

    Z.

Children
No Data