5.2.8.5 Toilet facilities and changing rooms

For such a small paragraph in BS5266, I fend many questions with respect to when you must provide emergency lighting and when it should be supported with emergency lighting calculations.

I assume I am not alone in this, so I thought I would share my interpretation of the requirements. I could not find any information on when you would consider a multi-closet facility to have borrowed light, the assumption at the end is unfounded and my interpretation only. Comments appreciated.

[post comment] The original intend of this post was to find if this table helped simplify the process of determining the requirements for emergency lighting in bathrooms etc. The intent was not to discuss the design process, nor the question of what borrowed light is, or any other standard. 

Unfortunately, I am unable to delete the topic or close it.

Applicable for:    
Toilets    
Bathroom    
Showers    
Changing Rooms    
     
Use of SpaceProvision of Borrowed LightArea of SpaceEmergency
Lighting
Required
Calculation
Required
For Use by Disabled PersonsAll8m2 or lessYESNO
For Use by Disabled PersonsAllAbove 8m2YESYES
Single Closet FacilitiesWith Borrowed Light8m2 or lessNO-
Single Closet FacilitiesWithout Borrowed Light8m2 or lessNO-
Single Closet FacilitiesWith Borrowed LightAbove 8m2YESYES
Single Closet FacilitiesWithout Borrowed LightAbove 8m2YESYES
Multiple Closet FacilitiesWith Borrowed Light8m2 or lessNO 
Multiple Closet FacilitiesWithout Borrowed Light8m2 or lessYESNO
Multiple Closet FacilitiesWith Borrowed LightAbove 8m2YESYES
Multiple Closet FacilitiesWithout Borrowed LightAbove 8m2YESYES
Hotel Bathroom/EnsuitsWith Borrowed Light8m2 or lessNO-
Hotel Bathroom/EnsuitsWithout Borrowed Light8m2 or lessNO-
Hotel Bathroom/EnsuitsWith Borrowed LightAbove 8m2YESYES
Hotel Bathroom/EnsuitsWithout Borrowed LightAbove 8m2YESYES
     
Note: closet, wall and doors must allow borrowed light. Using standard partition sizes and typical minimum ceiling height this would include 300mm above, and 100mm below. Where closet cannot be provided with borrowed light then emergency lighting per closet should be provided.
  • Sparkingchip: 
     

    Meanwhile some clever git installed presence detectors to turn the normal lighting on and off without giving people time to do what they need to do.

    yep, that is a pet peeve…. And for best comic effect put the sensor pointing at the entrance, but the light over the cubicle. Then the user has to get up in mid production and move to the door and wave arms or something to get the lights back on.

    Or take a head torch.

    Mike,

  • Can Zoomup‍ , mapj1‍ and Sparkingchip‍ delete their jokes and off topic responses please?
  • Leigh, I don't believe that the standard applies to areas that have public access. See extract:

    eb03981c2f68134f9a4bcbbc3df2f5b5-original-image.png

    I also don't believe that hotel rooms should be provided with emergency lighting (although many do), typically referring to Section 5 in BS 5266.

    If you have particular clause that would suggest otherwise, I would appreciate the information.

  • Lyledunn, upon reflection I concur that a bathroom or an ensuite facility within a hotel room would not be provided with emergency lighting, irrespective of size. I will amend table to reflect.

    440b035e6b80db831eeb54bb4892e173-original-image.png

    However, all facilities exceeding 8m2 need to be provided with emergency lighting, even if for single use, even if it has borrowed light (excluding, hotel bedroom facilities).

    Happy to relook if you believe this should be interpreted differently.

  • Alexander McNair (www.mbd-uk.com): 
    Can Zoomup‍ , mapj1‍ and Sparkingchip‍ delete their jokes and off topic responses please?

    Go and stand in the corner boys, you have been very naughty. 1000 lines each, oh, and detention for a week.

    Z.

     

     

  • I am asking you to be on topic and be professional.

  • Alexander McNair (www.mbd-uk.com): 
     

    Lyledunn, upon reflection I concur that a bathroom or an ensuite facility within a hotel room would not be provided with emergency lighting, irrespective of size. I will amend table to reflect

    So if you are in the bath or shower covered in shampoo and the lights go out, as the fire alarm sounds, and you are plunged into darkness will that cause a hazard and delay escape?

    Z.

  • Alexander McNair (www.mbd-uk.com): 
     

    I am asking you to be on topic and be professional.

    We are, and have a sense of humour too.?

    Z.

  • I have concurred that using the IET forum is a complete waste of time and the professionalism shown here is akin to Facebook standard.

    It would be great to part of a strong professional group, unfortunately this is not it.

  • Alexander McNair (www.mbd-uk.com): 
     

    @Zoomup, Sorry, I don't believe that your posts are professional in anyway.

    Don't be sorry. Just ask yourself, what is the prime purpose of emergency escape lighting? Look at the wider picture.