5.2.8.5 Toilet facilities and changing rooms
For such a small paragraph in BS5266, I fend many questions with respect to when you must provide emergency lighting and when it should be supported with emergency lighting calculations.
I assume I am not alone in this, so I thought I would share my interpretation of the requirements. I could not find any information on when you would consider a multi-closet facility to have borrowed light, the assumption at the end is unfounded and my interpretation only. Comments appreciated.
[post comment] The original intend of this post was to find if this table helped simplify the process of determining the requirements for emergency lighting in bathrooms etc. The intent was not to discuss the design process, nor the question of what borrowed light is, or any other standard.
Unfortunately, I am unable to delete the topic or close it.
Applicable for:
Toilets
Bathroom
Showers
Changing Rooms
Use of SpaceProvision of Borrowed LightArea of SpaceEmergency
Lighting
Required
Calculation
Required
For Use by Disabled PersonsAll8m2 or lessYESNO
For Use by Disabled PersonsAllAbove 8m2YESYES
Single Closet FacilitiesWith Borrowed Light8m2 or lessNO-
Single Closet FacilitiesWithout Borrowed Light8m2 or lessNO-
Single Closet FacilitiesWith Borrowed LightAbove 8m2YESYES
Single Closet FacilitiesWithout Borrowed LightAbove 8m2YESYES
Multiple Closet FacilitiesWith Borrowed Light8m2 or lessNO
Multiple Closet FacilitiesWithout Borrowed Light8m2 or lessYESNO
Multiple Closet FacilitiesWith Borrowed LightAbove 8m2YESYES
Multiple Closet FacilitiesWithout Borrowed LightAbove 8m2YESYES
Hotel Bathroom/EnsuitsWith Borrowed Light8m2 or lessNO-
Hotel Bathroom/EnsuitsWithout Borrowed Light8m2 or lessNO-
Hotel Bathroom/EnsuitsWith Borrowed LightAbove 8m2YESYES
Hotel Bathroom/EnsuitsWithout Borrowed LightAbove 8m2YESYES
Note: closet, wall and doors must allow borrowed light. Using standard partition sizes and typical minimum ceiling height this would include 300mm above, and 100mm below. Where closet cannot be provided with borrowed light then emergency lighting per closet should be provided.
  • I.E.T. "Electrician's Guide to Emergency Lighting 3rd Edition."
    A very useful publication.
  • What an odd thread! Topic posted and then matey seeks to moderate the thread. I newer did get the point. ?
  • He did seem to take exception a bit readily, good job he didn`t get one of my quips on his thread. Bit of friendly humour by some of those who contributed.
    Perhaps he is just a bit stressed at this time. It can happen to anyone of us.
    Anyway, if you are reading this mate then please do come back, we all like to help where we can
  • Withdrawn:
    Can Zoomup‍ , mapj1‍ and Sparkingchip‍ delete their jokes and off topic responses please?
    In what way is my response either a joke or off-topic ?
    It is neither. Seriously.
    Your  subject is electric lights in toilets, yes ? There are a great many examples where this is not done well, and to share ways to improve this with a wider  audience is my intention. You may not care for my posting style - that is entirely your choice, but I assure you I am being serious.
  • Exactly. As my therapist said about me, I may be bonkers, but I don't bite.
  • I did some work for the managing director of a lighting manufacturer at his home, including fitting one of his companies self testing emergency lights in his utility room.
    We had suite an involved discussion about emergency lighting and one of his comments was that self testing emergency lights in hotel bedrooms are not a good idea.
    Regards borrowed light, I had an architect telling me there’s no such thing when I was discussing emergency lighting design.
  • When I installed emergency lighting in a pubs toilet with two cubicles I simply placed the light above the intersection of the partitions so it throws light down into all three areas.
    Three emergency lights would have been completely over the top.
  • Presumably there’s a list of definitions in the standard, how does it define “borrowed light“?
  • Sparkingchip:
    Apparently, according to B.S. 5266-1 “Borrowed light" is defined as light obtained from an adjacent reliable source that is expected to be available at all material times. e.g from a local emergency luminaire.
  • Sparkingchip:
    That was my suggestion above, rather than relying on light being available above partitions or under closet doors, where much shadow would be created and irregular illumination.