There is an article in PE and I have just received it via email.
I am disappointed that the article seems to suggest that it contains all you need to know yet no mention is made of earthing systems
But also, this is only the earth electrode resistance, not the effective resistance from the transformer earth to the point at which you are standing …
Which is probably just what you want if you want to calculate the voltage between the MET and the ground at the consumer's installation - it's less likely that the victim will have long enough arms to be touching part of the consumer's installation while stood next to the substation.
AJJewsbury:
where the fault current exceeds the residual operating current, the touch voltage may also exceed 50 V until the device trips.
But the touch voltage won't persist - as the RCD will trip.
My point being, that the RCD trip is based on dry conditions … may be suitable for wet, but NOT submerged (so, consider steps metal into pool or sauna, and fault in heater element.
Remember I was comparing the situation with the problem of perceived shocks on PME systems - due to voltage drop along PEN conductor in normal, non-fault, conditions.
We say to avoid PME partly because perceived electric shocks from the PEN conductor which can potentially be up to (say) 18.4V above Earth, yet we recommend a TT system - possibly TT'd an entire installation - where there's no guarantee that voltages of anything up to to 50V might persist.
The PME diverted neutral currents may persist indefinitely … and local RoEP in an open-PEN situation may persist for a very long time (although it probably varies within that period).
That's sort of where my thinking lies Andy … sort of.
I think the real answer is that there are pro's and con's to each of the earthing arrangements, and sometimes mixing them up in an installation may well introduce con's from one arrangement to con's from the other, so perhaps you may end up increasing the risk over leaving everything on the original earthing arrangement.
Hi all,
Just to let you know that the issue you saw with the shared-in links not being visible on Apple iOS devices has now been fixed. So if you're viewing the community on an iPhone or iPad etc then you should be able to view the rich content when links are shared in i.e. the related image and description should appear in the post.
Lisa
I might be talking out of my hat here, but why not combine both systems? Why not export PME via the swa and 3rd core, tie both together at both ends, the tie both to a rod at the destination end too? Belt & braces?
Otherwise, we need to be looking at siting the electrical apparatus, pump, water heater etc remotely from the tub and further isolating heated pumped water through the use of distilled water and the requisite length of plastic pipework.
That would still suffer all the disadvantages of PME earthing. Unless the rod had a ridiculously low resistance to Earth (<< 1 Ohm) you'd still risk a hazardous potential on the earthing system during an open PEN event and the rise in potential of the soil around the rod would likely be far too steep to provide anything like equipotentiality in the vicinity of the tub. A buried grid under the entire area would probably be the minimum if you were going for that sort of approach.
AJJewsbury:
Andy,
How does the 1 ohm that align with the NOTE in 702.410.3.4.3, which says 20 ohms, and only a "mat or electrode' - not a grid? I do accept that there's a difference between BS 7671 and G12/4 in that the latter discussed a buried grid under zone 2 (implying exactly what you're saying), but that does not give earth electrode resistances … so would I still refer back to BS 7671 for that?
If one ohm is reasonable rather depends on the other impedances in the rest of the PME system fed from the same substation. 20 ohms may be a book figure, but to expect that to do much equalization against all but the weediest PME supply is optimistic in the extreme.
The supply to this hot tub is not like a 5A cut out feeding one streetlamp. The load of the hot tub heaters will be a few thousand watts, so in the range of 15-30 ohms itself. If in lost neutral fault we found just the hot tub, and not even the rest of the house, trying to return to ground via a 20 ohm electrode, all the exposed CPCs for the house would be well over the 50V safe limit for dry conditions. A hot tub user is unlikely to be to dry.
To be safe, rather than merely regs compliant, while wet and with one foot earthed ,you may prefer 25 volts at a likely diverted neutral current of perhaps 15- 20A. Not so far off the one ohm figure really.
It would be far safer if the supply to the hot tub was 3 phase of course, as then the neutral current would only be the imbalance of the phases, but to suggest 3 phase in a normal UK house that would bring out most domestic electricians and some DNO employees out in a nervous rash.