Consumer units and equipment outdoors

Hi,

Anything inherently wrong with installing consumer units outside? 

IP rated (IP65/66).

The plan is to install henley blocks into the exterior meter cupboard, and a supply taken to an IP rated lockable enclosure on the wall directly below the cupboard to supply an outbuilding.  

How does the sway in temperature impact MCB and RCD functionality? They all seem to be rated to sub zero temperatures and in excess of 40 degrees. 

Anyone with any extensive experience doing this? 
 

Thanks. 

Parents
  • Zoomup: 
     

    Always make a small drain hole at the lowest point. It allows natural aspiration and prevents condensation buildup. I try to use the bottom entry knockouts only. This is Chris's suggestion….

     

    BG Metal Garage Consumer Unit IP65 2 Way (toolstation.com)

    Z.

    Especially for outdoor installations, making a drain hole even 1 mm wide just lets insects in, or, in places exposed to wind, a lot of dust and detritus which, even in areas not by the coast, causes corrosion and early failure of equipment.

    I've seen the results in many installations. 

    The recommended approach is an IP55 drain plug (sometimes known as a “breather vent” or “vent drain”).

    Where enclosures require natural ventilation for cooling or to prevent accumulation of battery gas, one is fitted one side of the enclosure at the bottom or lower side, and another (with appropriate baffle or “periscope”) on the top or upper, at the opposite side.

Reply
  • Zoomup: 
     

    Always make a small drain hole at the lowest point. It allows natural aspiration and prevents condensation buildup. I try to use the bottom entry knockouts only. This is Chris's suggestion….

     

    BG Metal Garage Consumer Unit IP65 2 Way (toolstation.com)

    Z.

    Especially for outdoor installations, making a drain hole even 1 mm wide just lets insects in, or, in places exposed to wind, a lot of dust and detritus which, even in areas not by the coast, causes corrosion and early failure of equipment.

    I've seen the results in many installations. 

    The recommended approach is an IP55 drain plug (sometimes known as a “breather vent” or “vent drain”).

    Where enclosures require natural ventilation for cooling or to prevent accumulation of battery gas, one is fitted one side of the enclosure at the bottom or lower side, and another (with appropriate baffle or “periscope”) on the top or upper, at the opposite side.