This discussion is locked.
You cannot post a reply to this discussion. If you have a question start a new discussion

13A 1362 fuses and flex

Good evening everybody. 

I've been cogitating on the fusing factor of 1362 fuses (specifically 13A fuses)  and how this correlates with the protection of a 1.5mm2 flexible cable. As ever I am hoping you can shine a light!

The code of practice for the in service inspection and testing of equipment  Table 15.6 states that for flexes to be protected by the fuse in a BS1363 plug there is no limit to their length providing that their csa's are as in table 15.6 which states a minimum flex size of 1.25mm when using a 13A fuse. I am minded that it is quite common site to see a multi-gang extension lead on sale using 1.5mm2 flex where there is obviously potential for overload given the unknown nature of what would be plugged into them (even though there will be a warning not to intentionally do so).

From the Beama guide:

2.5 The BS1362 Fuse
The UK uses a fused plug which must be fitted with a BS 1362 fuse. For domestic
installations the use of the BS 1363 plug and socket system and the fitting of a BS 1362 fuse
into a plug is a legal requirement under the UK Plug and Socket Safety Regulations, 1995.
With a correctly fused BS 1363 plug, the flexible cable connected to equipment is always fully
protected against the effects of overload or small overcurrents as follows:
3A fuse protects 0.5mm² cords
5A (6A) fuse protects 0.75mm² cords
13A fuse protects 1.25mm2 cords
Protection against excessive damage by a short circuit is still achieved even if the smaller
cord sizes are inadvertently protected by a 13A fuse. In addition, it has been accepted in the
UK that some marginal damage to small flexible cords is tolerable under short circuit
conditions, for example where a 0.22mm² cord is used with a 13A BS 1362 fuse.

As far as I understand it the fusing factor of a 1362 fuse BS 1362 fuse is 1.9 (0.763) although in fairness I have seen lower fusing factors quoted (1.66?? which removes the particular problem I am wrestling with.)

Reference 4F3A a 1.5mm2 single phase AC flexible cable has a tabulated current carrying capacity of 16amps. 16x0.763 = 12.208 amps which is obviously less than the 13 amp rating of the fuse. 

I find it quite common to see 13A 1362 fuses inline on 32A cooker circuits protecting 1.5mm2 flexes to ovens. Is this deemed acceptable even though the oven isn't strictly speaking a fixed load (fan motor etc.)?

Is there another factor at play here which I am missing? Or do I just have the wrong fusing factor!

Thanks for your help in advance.

Parents
  • Realistically, a BS1362 fuse will protect the flex in the event of a short circuit in the appliance.  The fuse will blow before the cable melts.

    But it won't prevent long-term overloads.  A single appliance (including an oven) should never overload the flex if the manufacturer designed it right.  But a BS1362 fuse will not prevent long-term overloads on multi-way extension leads.

    It's no worse than in other countries in that respect.  In the USA, power circuits may have a 20A breaker.  But the individual plugs are only rated 15A for short-term loads.  And they have no fuses in the plugs at all.

Reply
  • Realistically, a BS1362 fuse will protect the flex in the event of a short circuit in the appliance.  The fuse will blow before the cable melts.

    But it won't prevent long-term overloads.  A single appliance (including an oven) should never overload the flex if the manufacturer designed it right.  But a BS1362 fuse will not prevent long-term overloads on multi-way extension leads.

    It's no worse than in other countries in that respect.  In the USA, power circuits may have a 20A breaker.  But the individual plugs are only rated 15A for short-term loads.  And they have no fuses in the plugs at all.

Children
No Data