13A 1362 fuses and flex

Good evening everybody. 

I've been cogitating on the fusing factor of 1362 fuses (specifically 13A fuses)  and how this correlates with the protection of a 1.5mm2 flexible cable. As ever I am hoping you can shine a light!

The code of practice for the in service inspection and testing of equipment  Table 15.6 states that for flexes to be protected by the fuse in a BS1363 plug there is no limit to their length providing that their csa's are as in table 15.6 which states a minimum flex size of 1.25mm when using a 13A fuse. I am minded that it is quite common site to see a multi-gang extension lead on sale using 1.5mm2 flex where there is obviously potential for overload given the unknown nature of what would be plugged into them (even though there will be a warning not to intentionally do so).

From the Beama guide:

2.5 The BS1362 Fuse
The UK uses a fused plug which must be fitted with a BS 1362 fuse. For domestic
installations the use of the BS 1363 plug and socket system and the fitting of a BS 1362 fuse
into a plug is a legal requirement under the UK Plug and Socket Safety Regulations, 1995.
With a correctly fused BS 1363 plug, the flexible cable connected to equipment is always fully
protected against the effects of overload or small overcurrents as follows:
3A fuse protects 0.5mm² cords
5A (6A) fuse protects 0.75mm² cords
13A fuse protects 1.25mm2 cords
Protection against excessive damage by a short circuit is still achieved even if the smaller
cord sizes are inadvertently protected by a 13A fuse. In addition, it has been accepted in the
UK that some marginal damage to small flexible cords is tolerable under short circuit
conditions, for example where a 0.22mm² cord is used with a 13A BS 1362 fuse.

As far as I understand it the fusing factor of a 1362 fuse BS 1362 fuse is 1.9 (0.763) although in fairness I have seen lower fusing factors quoted (1.66?? which removes the particular problem I am wrestling with.)

Reference 4F3A a 1.5mm2 single phase AC flexible cable has a tabulated current carrying capacity of 16amps. 16x0.763 = 12.208 amps which is obviously less than the 13 amp rating of the fuse. 

I find it quite common to see 13A 1362 fuses inline on 32A cooker circuits protecting 1.5mm2 flexes to ovens. Is this deemed acceptable even though the oven isn't strictly speaking a fixed load (fan motor etc.)?

Is there another factor at play here which I am missing? Or do I just have the wrong fusing factor!

Thanks for your help in advance.

Parents
  • I assume your vacuum vessel is mirror lined so no radiation loss ?.

    Then I agree with the several mins figure for a 40 degree rise. The conductor only version is the basis of our old friend the adiabatic calculation, where it is so fast that the heat does not have time to stabilise to  a uniform temp throughout the PVC, so we pretend that no heat is lost to the insulation at all, as the temperature rise calculated that way is always a safe over estimate, so we safely under estimate the let-through energy the cable can stand.

    In reality only AWE or CERN will install a cable in vacuum like that, and of course any real cable will heat quite a lot more slowly.

    The heat up rates for the different mounting methods are variations on the problem of filling a leaky bath, with the complication that the rate of leak varies with the depth of water. Some things, like heating a 4 inch thick brick wall on one  side of the cable, have very long time constants, and others, like a cable sandwiched in between layers of something like Kingspan insulation are much closer to the ‘vacuum’ case, as the stuff has almost no heat capacity.

    Mike

     

Reply
  • I assume your vacuum vessel is mirror lined so no radiation loss ?.

    Then I agree with the several mins figure for a 40 degree rise. The conductor only version is the basis of our old friend the adiabatic calculation, where it is so fast that the heat does not have time to stabilise to  a uniform temp throughout the PVC, so we pretend that no heat is lost to the insulation at all, as the temperature rise calculated that way is always a safe over estimate, so we safely under estimate the let-through energy the cable can stand.

    In reality only AWE or CERN will install a cable in vacuum like that, and of course any real cable will heat quite a lot more slowly.

    The heat up rates for the different mounting methods are variations on the problem of filling a leaky bath, with the complication that the rate of leak varies with the depth of water. Some things, like heating a 4 inch thick brick wall on one  side of the cable, have very long time constants, and others, like a cable sandwiched in between layers of something like Kingspan insulation are much closer to the ‘vacuum’ case, as the stuff has almost no heat capacity.

    Mike

     