Achieving acceptable Zs on a final circuit.
Sorry, brain fog….existing three phase final circuit protected by a 63a type c mcb. Zs is well in excess of the tabulated value. Is it acceptable practice to put a BS88 fuse after the mcb (next to the db) to increase the maximum permitted Zs?
  • yes - if the fuse provides closer protection than the MCB- how is the cable supplying the 63A protected ?
    That will need at least 5 seconds cover...
  • Mcb is in the db. Thinking is to feed out to a fused disconnector immediately then out to the 63amp socket. Run is approx 45m. Using the mcb alone, Zs is way over.
  • Yes, but it will not make any significant difference. You still need to trip within 0.4 s i.a.w. 411.3.2.2 (i) and Table 41.1. Tables 41.2 and 41.3 show that you will be able to increase the Max Zs from 0.35 Ω to all of 0.36 Ω.
  • depends on how much  lower rating is the proposed fuse - but it has to be quite a bit smaller than the MCB to allow the higher Zs.
    Or fit an RCD of course...
  • Or, perhaps, apply supplementary bonding. Check for thermal compliance.
  • Or add an RCD?
  • The question is what is causing the high Zs? You need to understand this first. What is the Zs at the DB? What cable and how long?  I would not be surprised if the Zs at the DB is too high too, presumably its supply is a lot more than 63A?