Achieving acceptable Zs on a final circuit.

Sorry, brain fog….existing three phase final circuit protected by a 63a type c mcb. Zs is well in excess of the tabulated value. Is it acceptable practice to put a BS88 fuse after the mcb (next to the db) to increase the maximum permitted Zs?

Parents
  • The question is what is causing the high Zs? You need to understand this first. What is the Zs at the DB? What cable and how long?  I would not be surprised if the Zs at the DB is too high too, presumably its supply is a lot more than 63A?

Reply
  • The question is what is causing the high Zs? You need to understand this first. What is the Zs at the DB? What cable and how long?  I would not be surprised if the Zs at the DB is too high too, presumably its supply is a lot more than 63A?