Under Voltage release / relay for the final distribution board

Do under voltage release / relays are required for the final distribution board installed at the absolute bottom of the power stream? Any disadvantages by not providing it?

Parents
  • Why is an under voltage trip required ? Not usual IME.

    It is usual to provide an under voltage release for individual motors or machines when unexpected re-starting would be dangerous or damaging, but not usual to provide this for a feeder or distribution circuit at utilisation voltages.

Reply
  • Why is an under voltage trip required ? Not usual IME.

    It is usual to provide an under voltage release for individual motors or machines when unexpected re-starting would be dangerous or damaging, but not usual to provide this for a feeder or distribution circuit at utilisation voltages.