Adiabatic Lecture.

Dad my head hurts. Is this guy any good?

https://www.youtube.com/watch?v=eCqyvmRHBqw

Surely the R.C.B.O. would disconnect the supply within 20 to 30 mS with an earth fault, in reality Dad.

Z.

Parents
  • Not sure if you can make this out on this single phase installation. The Device is a 100A time delay 100mA RCD with a stated Im of 1000A. Upstream DNO 80A 1361 2B fuse. 
    Ipf is circa 2KA on both LtoN and LtoE. 
    My understanding of the IM value is that it relates to current in the live conductors and where a 100A RCD is used the upstream fuse should be one step down, in this case 80A. 
    There is no mention of the IdeltaM value on the device. Any thoughts?

Reply
  • Not sure if you can make this out on this single phase installation. The Device is a 100A time delay 100mA RCD with a stated Im of 1000A. Upstream DNO 80A 1361 2B fuse. 
    Ipf is circa 2KA on both LtoN and LtoE. 
    My understanding of the IM value is that it relates to current in the live conductors and where a 100A RCD is used the upstream fuse should be one step down, in this case 80A. 
    There is no mention of the IdeltaM value on the device. Any thoughts?