Cooker and shower on the same circuit

Hello everyone,

A few months back, a qualified electrician told me that a cooker and a shower can both be put on the same circuit; that doesn't sound right, surely loads using such a large amount of power must be on their own individual circuits?

I haven't been able to ask a question about this until now because I had difficulty logging into my IET account and had to get a new username and password for it.

Thank you,

Dasa

Parents
  • Yesterday I went to look at some electrical work completed by someone else.

    It is a long story and there’s actually a lot to consider, but in amongst other things he has run a 2.5 mm twin and earth cable out of the shower switch to a single socket for a washing machine.

    6.0 mm shower circuit run externally clipped direct and painted B40 MCB supplying a 8.5 kW shower and a washing machine.

    Any comments?

  • I wouldn't object to to both loads intermittently running off a B40, but I would object to the 2.5mm T&E cabled being protected by a B40.

Reply
  • I wouldn't object to to both loads intermittently running off a B40, but I would object to the 2.5mm T&E cabled being protected by a B40.