Cooker and shower on the same circuit

Hello everyone,

A few months back, a qualified electrician told me that a cooker and a shower can both be put on the same circuit; that doesn't sound right, surely loads using such a large amount of power must be on their own individual circuits?

I haven't been able to ask a question about this until now because I had difficulty logging into my IET account and had to get a new username and password for it.

Thank you,

Dasa

Parents
  • Yesterday I went to look at some electrical work completed by someone else.

    It is a long story and there’s actually a lot to consider, but in amongst other things he has run a 2.5 mm twin and earth cable out of the shower switch to a single socket for a washing machine.

    6.0 mm shower circuit run externally clipped direct and painted B40 MCB supplying a 8.5 kW shower and a washing machine.

    Any comments?

  • I wouldn't object to to both loads intermittently running off a B40, but I would object to the 2.5mm T&E cabled being protected by a B40.

  • This is a mathematical challenge for Chris. The mathematical chances of numerous permutations.

    1. Is the shower used at full heat setting or just half max. heat setting?

    2. How often will the washing machine be using its heating element during the time that the shower is being used.

    3. How likely is it that the shower will be used at max. heat setting whilst the washing machine heater is on?

    4. And then there are the unknown factors.

    5. Which horse will win the 2.30 at Ascot?

    Z.

  • What about the limiting/protecting 13 Amp plug fuse?

    Z.