Do current limiting MCBs differ from Type B, Type C MCBs?
Makers data is needed to see the I2t trends beyond the minimum called out by EN610009
Do you mean EN60898 (Or possibly 60947-2)?
Can't see the one you quoted, could be 61009 RCBOs or 61000 series for EMC, did find a range of RCBOs in Aus here 3 Pole 20A RCBO 10KA 30MA C Curve TYPE A (Busbar Type with Neutral Pigtail) - LSTO20C/003A (agmelectrical.com.au) but i think they added a 0 by mistake
Makers data is needed to see the I2t trends beyond the minimum called out by EN610009
Do you mean EN60898 (Or possibly 60947-2)?
Can't see the one you quoted, could be 61009 RCBOs or 61000 series for EMC, did find a range of RCBOs in Aus here 3 Pole 20A RCBO 10KA 30MA C Curve TYPE A (Busbar Type with Neutral Pigtail) - LSTO20C/003A (agmelectrical.com.au) but i think they added a 0 by mistake
We're about to take you to the IET registration website. Don't worry though, you'll be sent straight back to the community after completing the registration.
Continue to the IET registration site