Regulation stating a type AC RCD can not be upstream from a type A RCD

Hi

I found an EV charger today with built in type A RCD + RDC-DD connected to a type AC RCD in the consumer unit, the AC RCD is also protecting 3 other circuits including sockets. I know this is incorrect because the type AC RCD could be blinded by DC currents, but I am struggling to find a regulation to reference when providing information to the customer?

Thanks

Alan

Parents
  • I`ll vote for it being OK because you`ve cascaded both types so if the AC type is actually a problem (Jury out on that one perhaps) then it still has type A which should work (if both are DP switching) . If the AC one is , in reality, not really much of a problem then you might have mitigated failure risk to some degree too.

Reply
  • I`ll vote for it being OK because you`ve cascaded both types so if the AC type is actually a problem (Jury out on that one perhaps) then it still has type A which should work (if both are DP switching) . If the AC one is , in reality, not really much of a problem then you might have mitigated failure risk to some degree too.

Children
  • But the type A RCD is also protecting other circuits, including a socket circuit  which could still have no RCD protection. Sorry I missed this in the original post, will update.