Regulation stating a type AC RCD can not be upstream from a type A RCD

Hi

I found an EV charger today with built in type A RCD + RDC-DD connected to a type AC RCD in the consumer unit, the AC RCD is also protecting 3 other circuits including sockets. I know this is incorrect because the type AC RCD could be blinded by DC currents, but I am struggling to find a regulation to reference when providing information to the customer?

Thanks

Alan

Parents
  • So now a pump manufacturer has DC? leakage of 3.5mA or less but wants a type A? Please explain why that might be.

    Because modern A-rated pumps are full of power electronics?

       - Andy.

Reply
  • So now a pump manufacturer has DC? leakage of 3.5mA or less but wants a type A? Please explain why that might be.

    Because modern A-rated pumps are full of power electronics?

       - Andy.

Children
  • Being full of electronics is not the reason for leakage is it? That is a get out of jail excuse with zero merit!

  • I could use an equally good argument, that the fact that single-phase LV supplies in the UK are "polarized", having a neutral conductor, rather than being "centre-tapped to Earth" as in a split-phase single-phase supply, exacerbates the situation for electronics designers.

    This is because we have a "system" that includes the source of supply, the installation, and the connected product, and decisions made at any point in that "system" may well affect the design of other parts of the "system".