Regulation stating a type AC RCD can not be upstream from a type A RCD

Hi

I found an EV charger today with built in type A RCD + RDC-DD connected to a type AC RCD in the consumer unit, the AC RCD is also protecting 3 other circuits including sockets. I know this is incorrect because the type AC RCD could be blinded by DC currents, but I am struggling to find a regulation to reference when providing information to the customer?

Thanks

Alan

Parents
  • That link returns an error Z, I think you will have to go one page back to make it work. However I have a different idea, which I think should work. If the loop tester has a transformer core with a winding coupling the L and N conductors so that the loop test current is also induced in the neutral (or this is the way it is injected with this TX), then the RCD should not trip but one can measure the L-N current so the loop test value. Has anyone seen that in any kit?

Reply
  • That link returns an error Z, I think you will have to go one page back to make it work. However I have a different idea, which I think should work. If the loop tester has a transformer core with a winding coupling the L and N conductors so that the loop test current is also induced in the neutral (or this is the way it is injected with this TX), then the RCD should not trip but one can measure the L-N current so the loop test value. Has anyone seen that in any kit?