Hi To all. I do not have the Regs AMD2 yet so I cant check. Is this a mistake? in Onsite guide P211 .It says a) 20A for ring circuit A1 then on P210 Table H2.1 A1 ring 30 or32 A.
Hi To all. I do not have the Regs AMD2 yet so I cant check. Is this a mistake? in Onsite guide P211 .It says a) 20A for ring circuit A1 then on P210 Table H2.1 A1 ring 30 or32 A.
Thank you geoffd .I am fixing some defects following EICR done by others. I noticed that they picked up a ring circuit on 16A but did not on 20 A. So I thought I check but those 2 pages in Onsite guide confused me. I do not know this A1 20A is relevant in the book and do not see the point. Thank you
A1 is the standard ring final circuit - 30A/32A with 2.5mm² T&E cable.
It is not an A1 20A circuit. It is just that you are looking at the conductor size H2.3 section as well.
The two legs must be a minimum of 20A CCC (although it states that the minimum size (except MICC) must be 2.5mm²; this still relates to a BS3036 30A fuse being used).
I may have misunderstood, what exactly was the defect that was found? It cannot be the CPD rating, was it the cable CSA?
I may have misunderstood, what exactly was the defect that was found? It cannot be the CPD rating, was it the cable CSA?
Hi David
Sorry for the delay. The defect I found was a 20A MCB on a ring circuit..Thanks
Ozz, that is not a defect, and is perfectly permitted! There may be reasons why this is there, usually that some part of a ring is of a smaller cable size or there are too many sockets on a spur. I would point out that the onsite guide is completely useless for inspection, a very much higher standard of knowledge of the regs is required, and the onsite guide only contains a set of suggestions which may well be over-engineered but are "safe" without further consideration. A smaller Circuit Protective Device (CPD) is not in any way dangerous, although it could be nuisance, that is all.
David, This ring got 4 points served. 2x 1 KW wall heater,1 undersinK 10 L water heater( could you not confirm current as no access to) and 1 twin socket. I understand that you can design non Uk standard ring circuit but can you can guaranty no one will plug anything on