Name the breaker. (Dorman Smith BS3871 Type D).

I an trying to determine the maximum Zs for the spare 16 amp MCB with a 5 second disconnect time. 

The maximum Zs of the SWA distribution circuit will be less than 1.4 ohms using a third core as the CPC not including the armour, so it will be lower.

Edit- taking Ze as 0.8 ohms TNS.

professional-electrician.com/.../

Parents
  • I can’t see it was ever a consumer unit suitable for a flat, particularly as it appears to have a D16 MCB on the lighting circuits, there will be a recommendation to replace.

    The commercial premises the flat is over is a dentists, so I can see why some of the circuits downstairs could need Type D MCBs, but the flat actually has a separate DNO supply and suppliers meter, so is a completely separate installation, I just suspect the same electricians wired the whole building and wired the flat the same as downstairs. 

Reply
  • I can’t see it was ever a consumer unit suitable for a flat, particularly as it appears to have a D16 MCB on the lighting circuits, there will be a recommendation to replace.

    The commercial premises the flat is over is a dentists, so I can see why some of the circuits downstairs could need Type D MCBs, but the flat actually has a separate DNO supply and suppliers meter, so is a completely separate installation, I just suspect the same electricians wired the whole building and wired the flat the same as downstairs. 