Name the breaker. (Dorman Smith BS3871 Type D).

I an trying to determine the maximum Zs for the spare 16 amp MCB with a 5 second disconnect time. 

The maximum Zs of the SWA distribution circuit will be less than 1.4 ohms using a third core as the CPC not including the armour, so it will be lower.

Edit- taking Ze as 0.8 ohms TNS.

professional-electrician.com/.../

Parents Reply Children
  • Zoom

    Many thanks for the link as it is a very fine example of persons carrying out EICRs who do not know their amp from their elbow! They then go on to post their pearls of wisdom to others on forums, thus perpetuating  the lack of competence.

    I think I have Dorman Smiith data in the Great Book of Circuit Protection. They are BS 3871 devices so standard tables can be used. However a lot of them are Type 4 so the OEMs data sheet must be used.