Dear Team,

We have two power supply's 110VDC connected in parallel to each other. Power diodes are being used in both 110VDC power supply's. I can understand the use of diode in Positive supply, it can block the reverse current flow in other power source if one of Power supply voltage get drop or failed. But what is the sue of diode in negative supply of 110vdc. Pl refer the attached screen shot & share your valuable comments. 

Parents
  • You don't say much about the DC supplies PS-1 and PS-2 themselves.

    The diodes would definitely be required in some circumstances, e.g. mid-point earthed systems.

  • Hi, The 110VDC supply's are coming from two different Battery chargers. So here two different 110VDC supply connected in parallel to form the redundancy & further feeding to common DC load. 

  • How is the battery (or DC system) earthed? Positive, negative, mid-point, or unearthed?

    If the battery is mid-point earthed, then the diodes will be required as per a mid-point earthed source.

    It would be unusual for a secondary battery installation to be floating unless it's used with an inverter system? If it's used with an inverter system, then that is the reason for the diodes, as the DC system will "pivot" around supply neutral.

Reply
  • How is the battery (or DC system) earthed? Positive, negative, mid-point, or unearthed?

    If the battery is mid-point earthed, then the diodes will be required as per a mid-point earthed source.

    It would be unusual for a secondary battery installation to be floating unless it's used with an inverter system? If it's used with an inverter system, then that is the reason for the diodes, as the DC system will "pivot" around supply neutral.

Children