If an external high level air-con unit has a rotary isolator positioned next to it, is it good practice to wire the isolator so that it disconnects both L. and N. of the supply?
Z.
(b) possibly will be maintained by someone who may be accessing from outside the building (i.e. outside the influence of the main bonding) - and the risk of a potential difference between N and Earth (rather than PE / MET) is greater. The risk is
So on TN, especially PME, systems, if we're isolating the N, should we be isolating the PE conductor too?
- Andy.
So on TN, especially PME, systems, if we're isolating the N, should we be isolating the PE conductor too?
I think that's another debate all together, although there are precedents of access equipment being bonded for various reasons, especially scaffolding.
It's far more likely in many installations there will be a voltage on a Neutral conductor if the rest of the installation remains live - yes there's a chance of a voltage difference with PME .. and any other earthing system for that matter.
Just a thought that removing PE on equipment in a system like HVAC might make things worse for you by removing a parallel path for current, because there may be fortuitous earthing via other means (pipework etc.)
So on TN, especially PME, systems, if we're isolating the N, should we be isolating the PE conductor too?
I think that's another debate all together, although there are precedents of access equipment being bonded for various reasons, especially scaffolding.
It's far more likely in many installations there will be a voltage on a Neutral conductor if the rest of the installation remains live - yes there's a chance of a voltage difference with PME .. and any other earthing system for that matter.
Just a thought that removing PE on equipment in a system like HVAC might make things worse for you by removing a parallel path for current, because there may be fortuitous earthing via other means (pipework etc.)