Mobile or Transportable units: What is classed as a unit and the supply cable from an external supply to the unit?

We have recently modified transportable units to the configuration described in Figure 17.6 of BS 7671. These units are connected at various third party locations around the country, with different types of supply systems.

IET Guidance Note 7: 18th: Amendment 2: 14.4.2 TN system states A PME earthing facility shall not be used as the means of earthing for mobile and transportable units falling within the scope of this Chapter, except where: (a) the installation is continuously under the supervision of an electrically instructed person competent in such work; skilled or (b) the suitability and effectiveness of the means of earthing has been confirmed before the connection is made; or (c) the unit is located within, or outdoors on an upper storey or roof of, a building or structure containing the electrical installation which supplies the unit.

The note goes onto state: There are many installations in premises that are TN-C-S in form and ordinary persons will be most unlikely to understand and fulfil the requirements set out in (a) and (b) above. It is therefore recommended that the arrangements of Figure 14.6 are followed wherever an ordinary person is required to use, operate or connect a unit to a supply with unknown or uncertain earthing arrangement.

As we have understood the unit to include the electrical installation within it, does this mean the cable used to supply the unit (up to the primary side of the isolating transformer) could be connected to a PME supply provided the earthing system at the supply point provide by the third party is suitable and effective (Zs is acceptable and the RCD trips)?

Parents
  • How far away from the building earth does the unit earth need to be?

  • Far enough away to not be influenced by any local P.M.E. earthing from anywhere, and where a rod can be driven into the ground, so not on concrete I suppose. A flat earthing plate has been used under a vehicle wheel before. Perhaps the vehicle should be situated on a large rubber insulating mat! Or, perhaps the 4 stabiliser legs will act as earth electrodes on suitable ground.

    Z.

  • You want to avoid someone straddling a PD with a human body, so usually assumed to be arms lengths - 2 yds, or 2metres. Indirect connection via soles of feet, paving, wet soil and other randoms are not really something that can be covered for all cases in regulation writing, so some gumption is needed, but in general metal bits either need to be solidly connected so no great voltage develops, or far enough apart to be inaccessible from one another when the normal activity of the place is happening.

    Mike.

Reply
  • You want to avoid someone straddling a PD with a human body, so usually assumed to be arms lengths - 2 yds, or 2metres. Indirect connection via soles of feet, paving, wet soil and other randoms are not really something that can be covered for all cases in regulation writing, so some gumption is needed, but in general metal bits either need to be solidly connected so no great voltage develops, or far enough apart to be inaccessible from one another when the normal activity of the place is happening.

    Mike.