Mobile or Transportable units: What is classed as a unit and the supply cable from an external supply to the unit?

We have recently modified transportable units to the configuration described in Figure 17.6 of BS 7671. These units are connected at various third party locations around the country, with different types of supply systems.

IET Guidance Note 7: 18th: Amendment 2: 14.4.2 TN system states A PME earthing facility shall not be used as the means of earthing for mobile and transportable units falling within the scope of this Chapter, except where: (a) the installation is continuously under the supervision of an electrically instructed person competent in such work; skilled or (b) the suitability and effectiveness of the means of earthing has been confirmed before the connection is made; or (c) the unit is located within, or outdoors on an upper storey or roof of, a building or structure containing the electrical installation which supplies the unit.

The note goes onto state: There are many installations in premises that are TN-C-S in form and ordinary persons will be most unlikely to understand and fulfil the requirements set out in (a) and (b) above. It is therefore recommended that the arrangements of Figure 14.6 are followed wherever an ordinary person is required to use, operate or connect a unit to a supply with unknown or uncertain earthing arrangement.

As we have understood the unit to include the electrical installation within it, does this mean the cable used to supply the unit (up to the primary side of the isolating transformer) could be connected to a PME supply provided the earthing system at the supply point provide by the third party is suitable and effective (Zs is acceptable and the RCD trips)?

Parents
  • How far away from the building earth does the unit earth need to be?

    From the point of view of someone stood on the ground touching the outside of the unit, you'd want the electrode to be as close as possible to the potential of that particular piece of ground. Going to extra effort to ensure the unit's electrode is at 'true Earth' potential, when the ground the unit stood on isn't, feels counterproductive to me.

    Perhaps the question should be: how close to the unit does the electrode need to be....

    That said, I'm not sure the unit necessarily needs an Earth electrode in all circumstances - the chassis as a reference can often be sufficient (the unit on its own little planet as it were). Even Class 1 equipment used outside the unit would have some protection against shock under single fault conditions as the supply is isolated from Earth.

       - Andy.

Reply
  • How far away from the building earth does the unit earth need to be?

    From the point of view of someone stood on the ground touching the outside of the unit, you'd want the electrode to be as close as possible to the potential of that particular piece of ground. Going to extra effort to ensure the unit's electrode is at 'true Earth' potential, when the ground the unit stood on isn't, feels counterproductive to me.

    Perhaps the question should be: how close to the unit does the electrode need to be....

    That said, I'm not sure the unit necessarily needs an Earth electrode in all circumstances - the chassis as a reference can often be sufficient (the unit on its own little planet as it were). Even Class 1 equipment used outside the unit would have some protection against shock under single fault conditions as the supply is isolated from Earth.

       - Andy.