Re: One month to go until BS 7671:2018+A1:2020 is withdrawn….act now!

I have just reveived an email from "IET Wiring Regulations".  In it, it says:-

Do you carry out inspections for landlords?

If you are performing electrical inspections for landlords of rented properties you must ensure that the installation is inspected against the most recent version of BS 7671. Staying up to date is imperative.

Am I wrong, or is that totally false?  Looking at https://www.legislation.gov.uk/uksi/2020/312/regulation/2/made, it says:-

“electrical safety standards” means the standards for electrical installations in the eighteenth edition of the Wiring Regulations, published by the Institution of Engineering and Technology and the British Standards Institution as BS 7671: 2018(3);

So that is a specific version of the Wiring Regulations, and not the new 2020 one.

Parents
  • As I like to point out from time to time, the Landlord regs require two main things: (1) for the property to be compliant with BS 7671:2020 at all times, and (2) for a T&I to be carried out every 5 years by a competent person, and anything flagged that violates (1) needs to be fixed within 28 days. Nowhere does it say that the inspection must be to BS 7671. A qualified electrician could write a report detailing how well the wiring complies with the principles of Feng Shui and the landlord would have discharged their obligation under (2).

    In practise, since the landlord still has obligation (1), if they have any sense they will ask for the inspection to be done to the current BS 7671, then fix up anything which would make them fall foul of (1).

    There's also the issue that classifying things as C1/C2/C3/FI isn't actually a requirement for BS 7671 T&I - its not mentioned in Ch 65, only in A6, which is informative (although the form in A6 is to be taken as a model). And the government has also realised that virtually no house complies fully with BS 7671:2020, so in their guidance docs they say words to the effect of "don't worry about C3s, and touch wood, the council won't prosecute you".

Reply
  • As I like to point out from time to time, the Landlord regs require two main things: (1) for the property to be compliant with BS 7671:2020 at all times, and (2) for a T&I to be carried out every 5 years by a competent person, and anything flagged that violates (1) needs to be fixed within 28 days. Nowhere does it say that the inspection must be to BS 7671. A qualified electrician could write a report detailing how well the wiring complies with the principles of Feng Shui and the landlord would have discharged their obligation under (2).

    In practise, since the landlord still has obligation (1), if they have any sense they will ask for the inspection to be done to the current BS 7671, then fix up anything which would make them fall foul of (1).

    There's also the issue that classifying things as C1/C2/C3/FI isn't actually a requirement for BS 7671 T&I - its not mentioned in Ch 65, only in A6, which is informative (although the form in A6 is to be taken as a model). And the government has also realised that virtually no house complies fully with BS 7671:2020, so in their guidance docs they say words to the effect of "don't worry about C3s, and touch wood, the council won't prosecute you".