Bonding.

I am concerned about exposed-conductive-parts and extraneous-conductive-parts and bonding. If a metal road drain cover is located next to, and in reach of a metal street light column, should the two be bonded together?

Parents
  • should the two be bonded together?

    Not for LV installations. It might be different in special circumstances if we are considering HV installations (BS EN 50522/BS EN 61936-1) or considering rail traction supplies.

    In BS 7671, Reg 714.411.3.1.2 covers this precise scenario.

Reply
  • should the two be bonded together?

    Not for LV installations. It might be different in special circumstances if we are considering HV installations (BS EN 50522/BS EN 61936-1) or considering rail traction supplies.

    In BS 7671, Reg 714.411.3.1.2 covers this precise scenario.