Does This Comply?

Location: Loft.

Accessibility: Difficult.

Junction box made out of a double pattress and a blanking plate. All plastic.

Internal joints inaccessible.

Thoughts?

Z.

Parents
  • 513.1 Each connection to be accessible, so if the lid does not come off, it is not compliant. Unless of course it is marked (MF) - 526.3(vi).

  • The internals are only accessible with the cover removed. Normally inaccessible to loft visitors. The cover is removeable by removing the screws.

    Z.

Reply
  • The internals are only accessible with the cover removed. Normally inaccessible to loft visitors. The cover is removeable by removing the screws.

    Z.

Children
  • So it complies.

    If the JB was Not secured then that may be regarded as a non-compliance. depends on the traffic ...