EICR - does bathroom lighting outside zone 2 need to conform with IP rating and additional rcd protection?

Hi, I have received an EICR certificate with 2 C2s on bathroom lighting 1) Bathroom lighting does not conform to IP rating (note the lighting outside the zone based on published zoning guidance (low voltage spot light) but inspector insisted on ignoring the zoning guidance) 2) Bathroom lighting circuit is not connected to an RCD also supplementary bonding is not visible. 

Questions- 1) Are the C2s legitimate? As a layman, I find it difficult to understand why the inspector insisted on ignoring the bathroom zoning regulation (my ceiling is actually higher than most of the newer flat) . 2) Also how do I find out whether there is supplemental bonding in the bathroom lighting circuit (nothing is visible outside) - does it really warrant a C2 if I cannot prove that there is supplemental bonding (the lighting in my bathroom is low voltage (I don’t know what is the voltage but it is very dim) and is located outside zone) . 3) If the C2s are legitimate, how can I fix the issue with minimal cost? 

many thanks for your time in advance.

  • Actually, can anyone here tell me what are potential options to deal with the RCD protection for bathroom lighting (from most economical to most effective bearing in mind that my bathroom lighting is low voltage and there is no intention to change going forward) and the indicative cost range if possible? My inspector kept asking me to undertake remedial work with them but does not provide any quotation so they can issue a clean report and I  can’t really understand what are being said in several messages above (pardon my ignorance). Many thanks 

  • It is not the lights themselves that require the RCD so the type doesn't matter.

    It is the circuit of a bathroom that might need the RCD..

  • Thanks - to summarise:

    1) any bathroom lighting circuit needs to have either RCD protection or supplemental bonding. There are no exception to the rule even if low voltage lights are in place and the flat is built 15 years ago and potentially there may be mitigating measures in place to support why no supplemental bonding is in place ( I can’t tell whether there is or not). Correct?

    2) Therefore the key is to establish whether there is supplemental bonding in the bathroom lighting circuit as it is not rcd protected. And I don’t have a clue whether there is or not - the inspector claimed there isn’t based on visual inspection alone. I’m checking with my management office to see if they have any clues. Meanwhile can kind souls enlighten me as to how inspectors typically check this point if supplemental bonding is not visible outside? Can they just assume there isn’t as long as they can’t see with their eyes?

    3) Nothwithstanding point 2, what potential options I have to remedy the RCD protection for bathroom? Time is bad now so I am afraid I really can’t afford something expensive but still I don’t want to be pound foolish and risk having to come back at fixing things later on. So can someone be kind enough to tell me say 1-3 options, rough estimate and how best to get reliable engineers to do the work?

    Many, many thanks. I’m really grateful because you guys are so ready to help shed lights on these matters (I have zero knowledge and had to do a lot of reading to gain a bit of understanding). Thanks again

  • It appears that a blanking piece in the lid of the CU is missing. There might be a 9 mm gap at either end, but that is really an 18 mm gap 'cos the pieces could easily be slid to one side. Assuming that a British Standard finger could reach the busbar (not visible in the photos), that's a C1.

  • Or just move the circuit to the RCD-protected half.

  • RCD options.

    1) as Chris P suggested, just move the lighting circuit to be under the protection of the RCD that is already there. The lighting breaker moves along the box a few places and the blanking plates (bits of plastic covering the un-used slots ) re-arrange.Cost is only labour, but it does mean if the sockets trip the RCD you lose lights as well, so cheap but not the finest.

    2)  An extra RCD is purchased and fitted in the box, there is  room, and the labour is about the same as above. Now lights and power are not tripping the same one.

    3) An RCBO is fitted in place of the lighting breaker (an RCBO is an RCD/breaker combo.) Takes up less space in the box and looks neater - is probably what you would do from new nowadays, Pricier than 1, or 2.

    4) An RCD just for the lights is put in a new little box alongside. Ugly but useful if the existing box is full or you know that it will be changed soon anyway, or if parts that fit the original are unobtainium for some reason.

    Bonding, should be verified by ohm meter. Standard process when it is boxed in. No need to see concealed wiring if it all measures OK.

    The lights may be 15 years old but they are not any less safe than when put in, and many folk would not blink, a C3 perhaps, but a C2 seems OTT unless there is a good reason we cannot see from the pics.'do not like the look of it' is not the same as 'fails reg xyz because'

    In your shoes I'd like to see the latter sort of justification - ask for the paragraph number of the reg it fails, and why. He is testing to BS7671, each paragraph has a no. for exactly  this reason. There really should  not be a lot of room for interpretation.

    Mike.

    edited for grammar typo

  • Many thanks - this is extremely useful. Any idea what could be reasonable labour cost and cost of 3 and 4?

    On the lighting point - he did said it could be c3 but he said he will still classify as C2 as it is what he usually does and he wants to stick to that. (He said someone can climb and stand above the edge of the shower and stretch to reach the light so it is within zone).

    On the supplemental bonding - he said visual inspection is sufficient - if it is not seen, then assume not present, again  based on his inspection experience.

    overall, it seems that the inspector is adamant to apply his usual practices on my EICR inspection. Initially he told me to just accept the conclusions and do not raise any feedback to anyone and he will do the work and reissue a clean certificate (but he didn’t provide any quotation despite various chasers and C2s are supposed to be time bound so I had to state my reservations with the landlord certificate services . when the inspector learnt this he would not entertain any enquiries anymore).

  • How do I address this? Thanks 

  • Oh dear. My  opinion of the guy is falling. Silent fixes, did he suggest payment in used fivers as well ?

    It should always be made very clear that unless you really know the guy well, that any remedials will not be done by the same outfit as the inspection.
    Otherwise there is a great temptation to make work by failing easy things to do, and not to bother to fail things that are really wrong and need doing, but are jobs that involve  more effort as they are awkward and less profitable to actually do.

    In other posts in this forum over the years we have read of some absolute corker examples of this sort  of thing happening.

    The agency that found him for you are missing a serious trick if they have not realised this is a temptation too far for some less scrupulous operators.

    Costs. Hard to say how much someone would quote, As well as the job itself which may vary with things we cannot see like how hard the walls are and the lengths  of slack in the cables,  it will depend on how far they have to drive and how busy as well as area factors like how easy and much it costs to park nearby - time is money and if you have to walk in for hundreds of yards and up 3 flights of stairs 3 times  lugging tool boxes only to look down out of the window and see someone scruffy type trying to break into the van it tends to put the prices up for that area next time. Some folk are wary of rented as not all tenants are actually reliably in or very welcoming even if the landlord has arranged it.

    Parts wise £ 50-100 of bits  and the bigger cost is perhaps half a day of actually being there at however many pounds an hour.  Your best bet is to try and call a few local sparks and see what they say, but good ones will probably want to see it or at least know a lot more before fixing a price - others may just over estimate and pocket the difference.

    Mike

  • Perhaps you might like to post a link to the actual report supplied, that would be most interesting, or if you don't want to do that a copy to me at davezawadi(at)yahoo.co.uk, it would be seen by some of the right people. Looking at the pictures, it looks pretty much like a contractor job at build time, since then there have been some changes to the regulations, but it is very unlikely there is much wrong as it will be the same for all the flats.

    I am interested that the management do not want to follow this up, as I personally consider this EICR inadequate as I have said above. If the same is happening to all the owners it certainly needs attention.

    I am interested particularly in the measurements results sheet and tick list of the report. I expect that you were not present when the work was done, but I would also like to know what other inspections were carried out, particularly of the tightness of all connections, as I suspect this was way too much trouble for this Inspector.

    You have verified that the lighting is ELV, so the C2 provided was false, as the non-compliance with 701 as I noted above.