PV flush downleads

New 3-storey house. PV panels on roof and inverter in garage on ground floor. Not unreasonably the client wants the downleads flush mounted. The proposal was to flush mount them in the masonry walls in steel conduit for the route from the loft area, down through bedroom on the top floor and TV room on first floor to garage on ground. No through boxes or the like to indicate cabling below. This is not a one-off situation as the client has a site of 40+ units. Done carefully, I can’t see too much of an issue but I just feel a tad uncomfortable. Any views?

Parents
  • well if you have earthed steel conduit, regs wise you are fine pretty much where ever you run it, and if it is ever drilled it can be re-threaded. Over a very long straight length you may need a larger diameter then first expected to be truly re-threadable.

    In your shoes I'd still aim near to be near but not quite in an internal corner where things are less likely to be casually screwed to the wall.  Or outside behind the drain pipes assuming it has some of those ;-)
    Mike.

Reply
  • well if you have earthed steel conduit, regs wise you are fine pretty much where ever you run it, and if it is ever drilled it can be re-threaded. Over a very long straight length you may need a larger diameter then first expected to be truly re-threadable.

    In your shoes I'd still aim near to be near but not quite in an internal corner where things are less likely to be casually screwed to the wall.  Or outside behind the drain pipes assuming it has some of those ;-)
    Mike.

Children
  •  "Or outside behind the drain pipes assuming it has some of those ;-)" until replacement drainpipe fitted just slightly off the original course of fixing brackets Wink