As per BS 7671, is it acceptable to use 4 cores (Br Bl Gy & Yellow) 300/500V cable be used for 3-phase motors?
What is the recommended voltage rating of power cables for three-phase motors?
Thanking you in advance.
The IET is carrying out some important updates between 17-30 April and all of our websites will be view only. For more information, read this Announcement
Power Supply - 3 Phase 400V
As per BS 7671, is it acceptable to use 4 cores (Br Bl Gy & Yellow) 300/500V cable be used for 3-phase motors?
What is the recommended voltage rating of power cables for three-phase motors?
Thanking you in advance.
Voltage ratings for cables are RMS voltages, not peak. 300/500 volt cable is intended for use on systems with up to 300 volts to earth or 500 volts between conductors.