As per BS 7671, is it acceptable to use 4 cores (Br Bl Gy & Yellow) 300/500V cable be used for 3-phase motors?
What is the recommended voltage rating of power cables for three-phase motors?
Thanking you in advance.
The IET is carrying out some important updates between 17-30 April and all of our websites will be view only. For more information, read this Announcement
Power Supply - 3 Phase 400V
As per BS 7671, is it acceptable to use 4 cores (Br Bl Gy & Yellow) 300/500V cable be used for 3-phase motors?
What is the recommended voltage rating of power cables for three-phase motors?
Thanking you in advance.
Cable voltage ratings (a/b volts) are a) to Earth and b) between cores, and as 400V 3-phase is 400V between lines and 230V between any line an N or Earth, then 300/500V cable should be adequate.
- Andy.
Being picky & pedantic.....
Are these (cable) ratings intended to be rms or peak?
One could argue that 230V rms (to earth) is really 230 * sqrt(2) = 325V since the cable insulation will be exposed to the peak of the sinewave.
Equally, 400V rms line-line is 565V peak.
Sooo... shouldn't we be talking about a 400/600V cable?
Are these (cable) ratings intended to be rms or peak?
I'd hope they were rms (like most things a.c.) - if not a lot of people are in a lot of trouble...
- Andy.
Though I might add that voltage rating isn't the only consideration - things like physical robustness may be needed for some environments, which usually implies a "chunkier" cables - which often naturally come with a higher voltage rating due to the thicker layers of insulation and sheath.
- Andy.
Nobody else has mentioned the use of the green & yellow core as a phase conductor.
I hadn't seen that suggestion - I thought the OP was suggesting Brown/Black/Grey for the lines, and (Green/)Yellow for PE - balanced loads like motors often don't need a N.
Re-using a G/Y core in a multicore cable as a live conductor isn't actually prohibited these days (likewise using a "line" coloured core as PE - which carries the same risks, if at the opposite end) - usually the problem is consequential the lack of a c.p.c. which is usually mandatory even when supplying double insulated equipment. For SWA however the armour could be used.
- Andy.
Oops. I misread the original post! I read it as brown, blue and green+yellow.