Temporary Connection of Generator to Domestic Distribution System

Hi All,

I recently came across a very interesting article - link below:

https://electrical.theiet.org/wiring-matters/years/2020/82-september-2020/mythbusters-6/

Where I find this article very interesting, is in relation to the requirement / or potentially non-requirement  of an Earth Spike, for the Temporary connection of a Generator to a building (in the article a Site Office is mentioned).

Please refer to the attached rough sketch / scheme for the Temporary Connection of Generator to Domestic Distribution System, which was originally based upon Figure 4 from the linked article - I wonder whether this could be considered, at least in principle, to be an appropriate proposal for the temporary connection of a generator to a domestic premises? In the attached scheme, there is no Earth Spike, and a 30mA RCD is included at the output of the generator, which would be connected to the generator via an appropriately sized SWA Cable. I would consider the potential for some nuisance tripping of the upstream 30mA RCD (in reality, this would be a rare occurrence) to be an acceptable price to pay, for the added protection that it would provide.

I would very much appreciate, if any of you could possibly find a moment or two, in order to share your thoughts in relation to the above / attached.

Thanks,

Harry G.


Parents
  • The SWA before the generator's RCD looks a little odd to me - usually SWA is chosen because of risk of mechanical damage and the usual mechanism is to earth the armour and use ADS to provide shock protection. It's not usual to rely on the SWA as mechanical protection alone.  In this case there are no conventional protective devices to provide ADS, so at best you'd be relying on stalling the generator (or at the very least hoping that the generator voltage output would collapse) due to the fault and the N-PE link at the far end of the SWA forming a short circuit. All of which may well happen in the real world, but without some specific data about both the cable and generator, it's difficult to prove.

    I would think a  more robust approach would be to site the RCD as close as reasonably practical to the generator and use a Class II (double/reinforced insulation) approach between the two - say insulated & sheathed singles in insulating conduit. All depending on the actual conditions of course. You could then use SWA after the RCD if you wish (to the socket or change-over switch).

    But yes, permanent attachment of a local electrode to the MET brings it all in line with usual practice. BS 7430 I think still recommends it has a maximum resistance to Earth of 20Ω, but that can be reasonably difficult to achieve and as long as you're not supplying any TT installations (e.g. outbuildings with their own separate earthing facilities) significantly high higher values are likely to be perfectly adequate in practice.

        - Andy.

Reply
  • The SWA before the generator's RCD looks a little odd to me - usually SWA is chosen because of risk of mechanical damage and the usual mechanism is to earth the armour and use ADS to provide shock protection. It's not usual to rely on the SWA as mechanical protection alone.  In this case there are no conventional protective devices to provide ADS, so at best you'd be relying on stalling the generator (or at the very least hoping that the generator voltage output would collapse) due to the fault and the N-PE link at the far end of the SWA forming a short circuit. All of which may well happen in the real world, but without some specific data about both the cable and generator, it's difficult to prove.

    I would think a  more robust approach would be to site the RCD as close as reasonably practical to the generator and use a Class II (double/reinforced insulation) approach between the two - say insulated & sheathed singles in insulating conduit. All depending on the actual conditions of course. You could then use SWA after the RCD if you wish (to the socket or change-over switch).

    But yes, permanent attachment of a local electrode to the MET brings it all in line with usual practice. BS 7430 I think still recommends it has a maximum resistance to Earth of 20Ω, but that can be reasonably difficult to achieve and as long as you're not supplying any TT installations (e.g. outbuildings with their own separate earthing facilities) significantly high higher values are likely to be perfectly adequate in practice.

        - Andy.

Children
  • Hi Andy,

    Thanks for the extra points for consideration.

    I have attached an annotated scheme here, which shows the 'nitty gritty' details of the installation, and may give some idea as regards the reasoning for my proposing SWA Cable upstream of the RCD (there is a 33A Circuit Breaker built into the generator - not sure of the precise trip characteristics). Possibly, it may be better to go with your suggestion of double insulated wiring upstream of the RCD - the reason that I had not done this, was I suppose, mainly relating to the increased mechanical robustness of the SWA Cable and Metal Enclosure for the RCD. 

    Also, I have attached a more simple scheme, without an RCD - I would say that in this case the SWA Cable between the Generator and Wall Mounted 32A Connector becomes a critical requirement?

    I'd be interested to receive your thoughts in relation to the above / attached.

    Best Regards,

    Mark G

    .

  • I'm struggling with to get any where near 20 ohms for a suitable means of earthing as per 551.4.3.2.1
    I'm in the Lakes difficult terrain at the best of times.
    A previous generator fitted had no alternative method of earthing at all.
    If we're looking at an Ra value of below 200ohms on a TT system what exactly are the perils of not achieving a 20 ohm figure?
    The generator 1ph 20kVa is I believe delivered with 30mA RCD as well as overload protection.

  • 20 ohms is a figure that derives from guidance for to substations and similar, and has no immediate physical significance. Of course in that case there is of course no RCD - there can't be as the DNOs permit PME. In the case of a single electrode for a private genset that is wired as TN-S there really is no risk from a rather higher electrode resistance. It would be good to trip the largest earthling leakage trip without passing 50V however, ideally with a good margin, so if you have 300mA or 100mA RCDs then you may need to stay in the low hundreds of ohms.

    Mike.

  • I'm wading my way through BS7430 as we speak!
    As I say Stephill the generator manufacturer have informed me that the generator is to be supplied with a 30mA RCD that could actually cause more selectivity problems than earthing problems on this old, much altered installation.Many thanks for your reply.