This discussion is locked.
You cannot post a reply to this discussion. If you have a question start a new discussion

Temporary Connection of Generator to Domestic Distribution System

Hi All,

I recently came across a very interesting article - link below:

https://electrical.theiet.org/wiring-matters/years/2020/82-september-2020/mythbusters-6/

Where I find this article very interesting, is in relation to the requirement / or potentially non-requirement  of an Earth Spike, for the Temporary connection of a Generator to a building (in the article a Site Office is mentioned).

Please refer to the attached rough sketch / scheme for the Temporary Connection of Generator to Domestic Distribution System, which was originally based upon Figure 4 from the linked article - I wonder whether this could be considered, at least in principle, to be an appropriate proposal for the temporary connection of a generator to a domestic premises? In the attached scheme, there is no Earth Spike, and a 30mA RCD is included at the output of the generator, which would be connected to the generator via an appropriately sized SWA Cable. I would consider the potential for some nuisance tripping of the upstream 30mA RCD (in reality, this would be a rare occurrence) to be an acceptable price to pay, for the added protection that it would provide.

I would very much appreciate, if any of you could possibly find a moment or two, in order to share your thoughts in relation to the above / attached.

Thanks,

Harry G.


Parents
  • I have attached an annotated scheme here, which shows the 'nitty gritty' details of the installation, and may give some idea as regards the reasoning for my proposing SWA Cable upstream of the RCD (there is a 33A Circuit Breaker built into the generator - not sure of the precise trip characteristics). Possibly, it may be better to go with your suggestion of double insulated wiring upstream of the RCD - the reason that I had not done this, was I suppose, mainly relating to the increased mechanical robustness of the SWA Cable and Metal Enclosure for the RCD. 

    Also, I have attached a more simple scheme, without an RCD - I would say that in this case the SWA Cable between the Generator and Wall Mounted 32A Connector becomes a critical requirement?

    I think you might be best taking a step back and have a think about general requirements - e.g. you need to provide shock protection (as per chapter 41) for each and every part of the system - so you need to consider how you achieve that - and in all reasonably possible circumstances - e.g. the generator is 'unplugged' from the installation while running (having the N-E link after the socket could undermine ADS for instance), and don't forget that all the normal rules still apply - e.g. fixed socket outlets rated <32A would need 30mA RCD protection (whereas a plug on the end of a lead which plugged into the generator wouldn't).

       - Andy.

Reply
  • I have attached an annotated scheme here, which shows the 'nitty gritty' details of the installation, and may give some idea as regards the reasoning for my proposing SWA Cable upstream of the RCD (there is a 33A Circuit Breaker built into the generator - not sure of the precise trip characteristics). Possibly, it may be better to go with your suggestion of double insulated wiring upstream of the RCD - the reason that I had not done this, was I suppose, mainly relating to the increased mechanical robustness of the SWA Cable and Metal Enclosure for the RCD. 

    Also, I have attached a more simple scheme, without an RCD - I would say that in this case the SWA Cable between the Generator and Wall Mounted 32A Connector becomes a critical requirement?

    I think you might be best taking a step back and have a think about general requirements - e.g. you need to provide shock protection (as per chapter 41) for each and every part of the system - so you need to consider how you achieve that - and in all reasonably possible circumstances - e.g. the generator is 'unplugged' from the installation while running (having the N-E link after the socket could undermine ADS for instance), and don't forget that all the normal rules still apply - e.g. fixed socket outlets rated <32A would need 30mA RCD protection (whereas a plug on the end of a lead which plugged into the generator wouldn't).

       - Andy.

Children
  • Hi Andy (and others that have previously provided helpful / much appreciated feedback),

    We are thinking that we may go with the arrangement shown in the attached picture.

    As regards the Earth Rod at the MET - I believe that this is a firm requirement, as per the Regs?

    Correct me if I'm wrong though - with this set-up, in reality, it is very unlikely that a fault could occur between Gen L1 and True Earth, as the Gen Frame is bonded to Gen L2 and also to all local Exposed and Extraneous Conductive Parts.

    What  am trying to say is, it is difficult to see how any contact could be made between Gen L1 and Earth, other than via the Gen Frame, which is already bonded to Gen L2.

    As always, any feedback would be much appreciated.

    Mark G.