Temporary Connection of Generator to Domestic Distribution System

Hi All,

I recently came across a very interesting article - link below:

https://electrical.theiet.org/wiring-matters/years/2020/82-september-2020/mythbusters-6/

Where I find this article very interesting, is in relation to the requirement / or potentially non-requirement  of an Earth Spike, for the Temporary connection of a Generator to a building (in the article a Site Office is mentioned).

Please refer to the attached rough sketch / scheme for the Temporary Connection of Generator to Domestic Distribution System, which was originally based upon Figure 4 from the linked article - I wonder whether this could be considered, at least in principle, to be an appropriate proposal for the temporary connection of a generator to a domestic premises? In the attached scheme, there is no Earth Spike, and a 30mA RCD is included at the output of the generator, which would be connected to the generator via an appropriately sized SWA Cable. I would consider the potential for some nuisance tripping of the upstream 30mA RCD (in reality, this would be a rare occurrence) to be an acceptable price to pay, for the added protection that it would provide.

I would very much appreciate, if any of you could possibly find a moment or two, in order to share your thoughts in relation to the above / attached.

Thanks,

Harry G.


Parents
  • That second sketch looks just the ticket and works for any supply earthing type- the electrode need not be a rod, if there is foundation piling or steelworks known to be in contact with the ground, go for it, but you would still need to test it like an electrode. 
    The new RCD can be a 100mA and with a 0.1s time delay  ('S' type) if you prefer to avoid one-out all-out tripping. This does limit the permitted installation methods a bit though, to surface wiring or things that are armoured or deep below the surface - no T and E or arctic flex under 5mm of polyfilla without a 30mA RCD!  I'm sure you would not, but I'm aware that others may read this website for inspiration.

    Mike.

  • Hi Mike,

    Thanks for your informative reply.

    I have attached an annotated scheme here, which shows the 'nitty gritty' details of the installation.

    Also, I have attached here a more simple scheme, without an RCD - I would say that in this case the SWA Cable between the Generator and Wall Mounted 32A Connector becomes a critical requirement?

    I'd be interested to receive your thoughts in relation to the above / attached.

    Best Regards,

    Mark G

  • I presume the '33A CB' relates to the breaker built into the genset controller  ?

    For any cable between that and the first  RCD you are reliant on a dead short to earth to operate that CB, as it is in effect an overcurrent device, not an ELCB.  So yes, SWA, or earthed metal conduit, are the options that can be shallow buried in the wall,  or if the route is visible, then reinforced insulation (like meter tail) or ordinary cables in  plastic conduits are your earth free options.

    Note Andy's comment about plugs and sockets without RCD protection - the one on the genset is part of the fixed kit and pretty much unavoidable, but try and avoid adding more if you can ; -)

    Given the lengths and the location, you have a number of sensible options just keep it simple enough that it can be maintained by someone else as well if ever need be.

    Mike

Reply
  • I presume the '33A CB' relates to the breaker built into the genset controller  ?

    For any cable between that and the first  RCD you are reliant on a dead short to earth to operate that CB, as it is in effect an overcurrent device, not an ELCB.  So yes, SWA, or earthed metal conduit, are the options that can be shallow buried in the wall,  or if the route is visible, then reinforced insulation (like meter tail) or ordinary cables in  plastic conduits are your earth free options.

    Note Andy's comment about plugs and sockets without RCD protection - the one on the genset is part of the fixed kit and pretty much unavoidable, but try and avoid adding more if you can ; -)

    Given the lengths and the location, you have a number of sensible options just keep it simple enough that it can be maintained by someone else as well if ever need be.

    Mike