Temporary Connection of Generator to Domestic Distribution System

Hi All,

I recently came across a very interesting article - link below:

https://electrical.theiet.org/wiring-matters/years/2020/82-september-2020/mythbusters-6/

Where I find this article very interesting, is in relation to the requirement / or potentially non-requirement  of an Earth Spike, for the Temporary connection of a Generator to a building (in the article a Site Office is mentioned).

Please refer to the attached rough sketch / scheme for the Temporary Connection of Generator to Domestic Distribution System, which was originally based upon Figure 4 from the linked article - I wonder whether this could be considered, at least in principle, to be an appropriate proposal for the temporary connection of a generator to a domestic premises? In the attached scheme, there is no Earth Spike, and a 30mA RCD is included at the output of the generator, which would be connected to the generator via an appropriately sized SWA Cable. I would consider the potential for some nuisance tripping of the upstream 30mA RCD (in reality, this would be a rare occurrence) to be an acceptable price to pay, for the added protection that it would provide.

I would very much appreciate, if any of you could possibly find a moment or two, in order to share your thoughts in relation to the above / attached.

Thanks,

Harry G.


Parents
  • Sorry for only spotting this a bit late and butting in.

    The reason for this (as recommended for one of the options for wiring systems in BS 7430) is clear if you think about a fault scenario of a severed cable. The generator can continue to run, but the protective conductor (providing connection to Earth, i.e. terra-firma itself) could well be broken. SWA is provided to help provide more mechanical protection, and increase the chance that, in a cable impact scenario between generator and installation, that the protective device at the generator will operate.

    An interesting point (never too late for interesting information!). Reading the wider context of BS 7430 though, there seems to be an assumption that the generator's in-built overload protection will provide ADS and any RCD is only for additional protection. I might also add that taking a recommendation from one standard isn't quite the same as showing compliance with a particular requirement of a different standard (e.g. Chapter 41 of BS 7671). I dare say that in most cases there will be some combination of either the generator's OCPD operating, or the generator mechanically stalling or just the limited current available together with a low loop impedance to the fault limiting any touch voltage, so that the risk of shock is eliminated. How you could demonstrate that that definitely would be the case and so meet  BS 7671 requirements could be more interesting, even if you go down the section 419 route (do generator manufacturers generally provide the necessary data?). As ever there's more than one way to skin a cat.

        - Andy.

Reply
  • Sorry for only spotting this a bit late and butting in.

    The reason for this (as recommended for one of the options for wiring systems in BS 7430) is clear if you think about a fault scenario of a severed cable. The generator can continue to run, but the protective conductor (providing connection to Earth, i.e. terra-firma itself) could well be broken. SWA is provided to help provide more mechanical protection, and increase the chance that, in a cable impact scenario between generator and installation, that the protective device at the generator will operate.

    An interesting point (never too late for interesting information!). Reading the wider context of BS 7430 though, there seems to be an assumption that the generator's in-built overload protection will provide ADS and any RCD is only for additional protection. I might also add that taking a recommendation from one standard isn't quite the same as showing compliance with a particular requirement of a different standard (e.g. Chapter 41 of BS 7671). I dare say that in most cases there will be some combination of either the generator's OCPD operating, or the generator mechanically stalling or just the limited current available together with a low loop impedance to the fault limiting any touch voltage, so that the risk of shock is eliminated. How you could demonstrate that that definitely would be the case and so meet  BS 7671 requirements could be more interesting, even if you go down the section 419 route (do generator manufacturers generally provide the necessary data?). As ever there's more than one way to skin a cat.

        - Andy.