Temporary Connection of Generator to Domestic Distribution System

Hi All,

I recently came across a very interesting article - link below:

https://electrical.theiet.org/wiring-matters/years/2020/82-september-2020/mythbusters-6/

Where I find this article very interesting, is in relation to the requirement / or potentially non-requirement  of an Earth Spike, for the Temporary connection of a Generator to a building (in the article a Site Office is mentioned).

Please refer to the attached rough sketch / scheme for the Temporary Connection of Generator to Domestic Distribution System, which was originally based upon Figure 4 from the linked article - I wonder whether this could be considered, at least in principle, to be an appropriate proposal for the temporary connection of a generator to a domestic premises? In the attached scheme, there is no Earth Spike, and a 30mA RCD is included at the output of the generator, which would be connected to the generator via an appropriately sized SWA Cable. I would consider the potential for some nuisance tripping of the upstream 30mA RCD (in reality, this would be a rare occurrence) to be an acceptable price to pay, for the added protection that it would provide.

I would very much appreciate, if any of you could possibly find a moment or two, in order to share your thoughts in relation to the above / attached.

Thanks,

Harry G.


Parents
  • I'm struggling with to get any where near 20 ohms for a suitable means of earthing as per 551.4.3.2.1
    I'm in the Lakes difficult terrain at the best of times.
    A previous generator fitted had no alternative method of earthing at all.
    If we're looking at an Ra value of below 200ohms on a TT system what exactly are the perils of not achieving a 20 ohm figure?
    The generator 1ph 20kVa is I believe delivered with 30mA RCD as well as overload protection.

    20Ω is a BS 7430 suggestion rather than a direct BS 7671 requirement. We have debate the logic of why 20Ω exactly a few times and there doesn't seem to be any particular maths to back it up - more that it's a useful convention - especially as it matches what the DNOs do. In that respect achieving 20Ω makes life easier in some ways - if you has your generator supplying your TN installation, but has a TT'd outbuilding hanging off it, if you matched the DNO's earthing characteristics you could be confident all would be well with the TT part when running off the generator.  If your electrode was substantially higher, then the TT installation would have to cope with much higher earth fault loop impedances - which might then compromise things (or at least demand that the design was re-checked).

       - Andy.

Reply
  • I'm struggling with to get any where near 20 ohms for a suitable means of earthing as per 551.4.3.2.1
    I'm in the Lakes difficult terrain at the best of times.
    A previous generator fitted had no alternative method of earthing at all.
    If we're looking at an Ra value of below 200ohms on a TT system what exactly are the perils of not achieving a 20 ohm figure?
    The generator 1ph 20kVa is I believe delivered with 30mA RCD as well as overload protection.

    20Ω is a BS 7430 suggestion rather than a direct BS 7671 requirement. We have debate the logic of why 20Ω exactly a few times and there doesn't seem to be any particular maths to back it up - more that it's a useful convention - especially as it matches what the DNOs do. In that respect achieving 20Ω makes life easier in some ways - if you has your generator supplying your TN installation, but has a TT'd outbuilding hanging off it, if you matched the DNO's earthing characteristics you could be confident all would be well with the TT part when running off the generator.  If your electrode was substantially higher, then the TT installation would have to cope with much higher earth fault loop impedances - which might then compromise things (or at least demand that the design was re-checked).