Temporary Connection of Generator to Domestic Distribution System

Hi All,

I recently came across a very interesting article - link below:

https://electrical.theiet.org/wiring-matters/years/2020/82-september-2020/mythbusters-6/

Where I find this article very interesting, is in relation to the requirement / or potentially non-requirement  of an Earth Spike, for the Temporary connection of a Generator to a building (in the article a Site Office is mentioned).

Please refer to the attached rough sketch / scheme for the Temporary Connection of Generator to Domestic Distribution System, which was originally based upon Figure 4 from the linked article - I wonder whether this could be considered, at least in principle, to be an appropriate proposal for the temporary connection of a generator to a domestic premises? In the attached scheme, there is no Earth Spike, and a 30mA RCD is included at the output of the generator, which would be connected to the generator via an appropriately sized SWA Cable. I would consider the potential for some nuisance tripping of the upstream 30mA RCD (in reality, this would be a rare occurrence) to be an acceptable price to pay, for the added protection that it would provide.

I would very much appreciate, if any of you could possibly find a moment or two, in order to share your thoughts in relation to the above / attached.

Thanks,

Harry G.


Parents
  • Going off on a tangent a bit ... with grid connected PV systems we provide ADS to the generator circuit by a downstream (from the point of view of the PV generator) double pole switching RCD (or 4P for 3Φ). That works even though we don't disconnect the PV generated voltage from the fault, the breaking of the N means that the PV generator's N is effectively isolated from Earth - forming a separated system - and so eliminating the shock risk that way.  I was just wondering if we could take a similar approach with a stand-alone (or switched alternative) generator - by placing an extra "Generator" RCD before the N-PE link, to provide shock protection for any exposed-conductive-parts (e.g. SWA) between the generator and RCD. The generator RCD could be relatively sensitive (30mA) say as it wouldn't see leakage or earth fault currents from the installation (they'd return to N via the N-PE link downstream of the - the generator RCD) - so the main RCD could sensibly be higher - 100mA or 300mA S-type say without loss of discrimination.

       - Andy.

Reply
  • Going off on a tangent a bit ... with grid connected PV systems we provide ADS to the generator circuit by a downstream (from the point of view of the PV generator) double pole switching RCD (or 4P for 3Φ). That works even though we don't disconnect the PV generated voltage from the fault, the breaking of the N means that the PV generator's N is effectively isolated from Earth - forming a separated system - and so eliminating the shock risk that way.  I was just wondering if we could take a similar approach with a stand-alone (or switched alternative) generator - by placing an extra "Generator" RCD before the N-PE link, to provide shock protection for any exposed-conductive-parts (e.g. SWA) between the generator and RCD. The generator RCD could be relatively sensitive (30mA) say as it wouldn't see leakage or earth fault currents from the installation (they'd return to N via the N-PE link downstream of the - the generator RCD) - so the main RCD could sensibly be higher - 100mA or 300mA S-type say without loss of discrimination.

       - Andy.

Children
  • As in a rough Restricted Earth Fault scheme built out of RCDs?

    (So would need care with, for example, saturation of CTs during out of zone faults, inrush harmonics etc)

    To avoid a loss of cover over the N-E link, one could also conceive the RCD being *downstream* of the link, but that’d need a 5P RCD (earth in a reverse direction) or more realistically an earth fault relay with all conductors going through a common toroidal/window CT at which point you might as well have a traditional REF.

  • An RCD before the N-E link never trips for any sort of fault to earth, between RCD and and the link, as it just looks like an additional load.    You may want breaking at that point you probably want the sensing that drives it somewhere else.

    Mike.