Good morning Guys,
I refer to Chapter 52 ( 521.9) of BS 7671, Can we use class 5 conductor ( multicore Cable) in fixed Installation for wiring lighting, power ? Grateful if someone can help answer with document evidence.
The IET is carrying out some important updates between 17-30 April and all of our websites will be view only. For more information, read this Announcement
Good morning Guys,
I refer to Chapter 52 ( 521.9) of BS 7671, Can we use class 5 conductor ( multicore Cable) in fixed Installation for wiring lighting, power ? Grateful if someone can help answer with document evidence.
Originally there was a flat prohibition on using flex for fixed wiring (apart from the final connection to fixed appliances) but that originated in the days when flex was much less substantial than premises wiring cables - typically being a couple of rubber singles with little more than a thin cotton braiding over. These days flexes have more robust PVC insulation and a PVC oversheath so apart from the conductor being stranded are pretty much identical and generally just as robust as rigid PVC/PVC cables.
- Andy.
Good afternoon Andy,
Thanks for Feedback. You comments are quite clear.
I am looking for backup where Class 5 flexible cable is clearly mentioned suitable for fixed installations. We follow BS 7671:2018 here. If we compare Class 02 versus Class 05. Class 02 conductor is known to be suitable for wiring at fixed installations. But certain projects demands for class 05 flexible conductors. I want to ensure that class 05 usage in fixed installation is good by norms.
I want to ensure that class 05 usage in fixed installation is good by norms.
Well, flexible cables (Class 5 and Class 6 stranding) are actually specified for some installations, or parts of installations, within BS 7671.
Flexible cables must be acceptable (if properly selected, erected and protected for the installation conditions - as with all cables), because:
Of course, when using stranded wires, appropriate terminals ought to be used, or, Class 5 or Class 6 conductors are to be terminated in terminals suitable only for Class 1 (solid) and/or Class 2 (stranded) they should be suitable prepared, for example with a ferrule. (See Regulation Group 526.9.)
Good morning Graham,
Really appreciated on above points shared. Indeed these were very helpful in getting quite clear on the different applications for class 05.
Though I noticed from your reply above that below regulations indeed can be used for installing the class 05 conductor ( Heavy duty Type having voltage rating of not less than 450/750V) for Fixed installation with Chris comments on adjustment is made for flexible cables in Table 4D2A.
Thanks & Regards,
Good morning Graham,
Really appreciated on above points shared. Indeed these were very helpful in getting quite clear on the different applications for class 05.
Though I noticed from your reply above that below regulations indeed can be used for installing the class 05 conductor ( Heavy duty Type having voltage rating of not less than 450/750V) for Fixed installation with Chris comments on adjustment is made for flexible cables in Table 4D2A.
Thanks & Regards,
when using stranded wires, appropriate terminals ought to be used, or, Class 5 or Class 6 conductors are to be terminated in terminals suitable only for Class 1 (solid) and/or Class 2 (stranded) they should be suitable prepared, for example with a ferrule. (See Regulation Group 526.9.)
This depends on terminal type.
to CENELEC standards: