Good morning Guys,
I refer to Chapter 52 ( 521.9) of BS 7671, Can we use class 5 conductor ( multicore Cable) in fixed Installation for wiring lighting, power ? Grateful if someone can help answer with document evidence.
Good morning Guys,
As in the Regulation, if the cable is protected against damage, then it is fine to be used.
Multiple inset downlights use flex, as, basically, the connection blocks for them do not have enough room for 2x 1.5mm T+E cables, so a JB, and a flex off to the fitting is the usual solution.
Originally there was a flat prohibition on using flex for fixed wiring (apart from the final connection to fixed appliances) but that originated in the days when flex was much less substantial than premises wiring cables - typically being a couple of rubber singles with little more than a thin cotton braiding over. These days flexes have more robust PVC insulation and a PVC oversheath so apart from the conductor being stranded are pretty much identical and generally just as robust as rigid PVC/PVC cables.
Good afternoon Andy,
Thanks for Feedback. You comments are quite clear.
I am looking for backup where Class 5 flexible cable is clearly mentioned suitable for fixed installations. We follow BS 7671:2018 here. If we compare Class 02 versus Class 05. Class 02 conductor is known to be suitable for wiring at fixed installations. But certain projects demands for class 05 flexible conductors. I want to ensure that class 05 usage in fixed installation is good by norms.
Well, flexible cables (Class 5 and Class 6 stranding) are actually specified for some installations, or parts of installations, within BS 7671.
Flexible cables must be acceptable (if properly selected, erected and protected for the installation conditions - as with all cables), because:
Of course, when using stranded wires, appropriate terminals ought to be used, or, Class 5 or Class 6 conductors are to be terminated in terminals suitable only for Class 1 (solid) and/or Class 2 (stranded) they should be suitable prepared, for example with a ferrule. (See Regulation Group 526.9.)
Good morning Graham,
Really appreciated on above points shared. Indeed these were very helpful in getting quite clear on the different applications for class 05.
Though I noticed from your reply above that below regulations indeed can be used for installing the class 05 conductor ( Heavy duty Type having voltage rating of not less than 450/750V) for Fixed installation with Chris comments on adjustment is made for flexible cables in Table 4D2A.
Thanks & Regards,
Good morning Chris,
Indeed your reply along with Graham's reply help me reach to my conclusion.
Since I don't have BS EN 50565-01 to understand real definition on described on Light, Ordinary, Heavy duty type. Grateful if you can help on same as well. This is part of regulation group 521.9 and 422.3.201. I want to clear my doubt on the definition by BS EN 50565-01.
The question is the mechanical robustness - flexible cables have the conductor stranded, and how many strands and how fine is the 'class' in this context, the insulation must be more or less flexible, but more flexible cables are more prone to mechanical damage (in simple terms the plastic or rubber scratches off more easily if it is soft, but if it is not soft it does not flex so well ).
So cables that get dragged over rough ground or concrete, or may be trodden on need harder plastic but are less flexible than those that are gently clamped against a smooth surface and just flex a bit.
However, for cable that is to reel in and out - as for example on certain types of machine, cranes and so on come to mind, the softer insulation and finer strands are essential. Then there is temperature - some plastics flexible at room temperature become brittle   a 'glass transition' when too cold and shatter if moved before heating up.
' heavy duty' cables are those that should survive abrasion and collision the best, 'light duty' is for environs more like indoors, clean, stable temperatures and  any handling there is not too rough.
medium is just everything else.
The regs are really saying 'consider these factors' when selecting your cable, as there is no single 'best answer' for all situations.
Not a clear cut yes no answer but maybe helps paint the picture.
Heavy duty describes the stresses that might be expected in, for example, industrial and agricultural premises
Ordinary duty describes the stresses that might be expected in, for example, domestic, commercial and light industrial applications.
Light duty applications might include flexible cables for small appliances
Extra light duty applications are, for example, very small appliances, for example electric shavers, chargers for mobile phones, etc.