Wiring on Fixed installation with class 5 conductor (Flexible Cable).

Good morning Guys,

I refer to Chapter 52 ( 521.9) of BS 7671, Can we use  class 5 conductor ( multicore Cable) in fixed Installation for wiring lighting, power ? Grateful if someone can help answer with document evidence.

  • when using stranded wires, appropriate terminals ought to be used, or, Class 5 or Class 6 conductors are to be terminated in terminals suitable only for Class 1 (solid) and/or Class 2 (stranded) they should be suitable prepared, for example with a ferrule. (See Regulation Group 526.9.)

    This depends on terminal type.

    to CENELEC standards:

    • Terminals that have no marking can be assumed to be suitable for all classes of conductor, although you might want to use ferrules for class 5 and class 6 stranded conductors if they are to be regularly disconnected and reconnected, or where installation and maintenance activities would be slowed down drastically by having to re-strip to reconnect (for example industrial control panels, alarm systems, etc.)
    • Terminals marked 'r' are suitable for rigid conductors (class 1 and class 2 only). Class 5 and Class 6 stranded conductors may be terminated if crimp ferrules can be used (although manufacturer's instructions should be followed for screwless terminals).
    • Terminals marked 'sol' are suitable for class 1 (solid) conductors only. If manufacturers instructions permit, class 2, 5 and 6 conductors might be connected using crimp ferrules.
    • Terminals marked 'f' may only be used for class 5 and class 6 stranded (flexible and extra-flexible respectively) conductors. Ferrules should not be used for Class 5 and Class 6 stranded conductors in terminals marked 'f'
  • Thanking you very much Graham for the reply. Grateful to clarify on the definition of heavy duty, Ordinary duty, Light duty cables based on BS EN 50565-01.

    Really appreciated your answer regarding the type of application these cables are in.

    Thanks & Regards,

    Satish Kumar

  • Thanks Graham for above explanation.

  • Really appreciated your answer regarding the type of application these cables are in.

    No problem - for once, this is pretty much paraphrased from the standard itself, which provides the real-world examples for these categories.