Neat job. New Domestic installation single-phase so really should be 4pole isolator. Any way, the BC officer has e pressed concerns about the mounting height. The board is tucked up close to the ceiling in a small plant room to allow room for a host of other bits and bobs including PV, battery, TV, intruder, IT equipment.
Now the BC officer hasn’t turned it down outright but you can imagine that it would be a pain to move. Even if it was dropped, the height of the RCBOs would still sit slightly outside the 1350 to 1450mm recommendation due to the height of the pan assembly.
Quite apart from a BC issue, since this is a new build, would it be reasonable to contend that it didn’t meet 7671 in that surely one must consider BA3?