Hi

I have to decide on a circuit breaker for a 22 KW, 3 phase 400V Air compressor. 
Load current = P / (1.732 * V *PF) =22000 /(1.732*400*0.8)
= 39.69A

Therefore a 40A Type D CB is used.

These are my questions:
1. Do we have to include the PF if not given in the equipment datasheet for current calculation.
2. Is this the right way to find the size of MCB? i will also be including an overload relay. Is there anything else i need to lookout for?

Thank you in advance for your help.

Parents
  • For a potentially long hour load, I would consider it good practice to size a fuse or an MCB at at least 110% of the calculated or stated running current, rounded up to the next standard size. This allows for supply voltage variations and manufacturing tolerances. So for a 39.6 amp load use a 45 amp fuse or MCB as a minimum.

    Additional upsizing may be required for motors due to the starting current. This depends on the starting method used, and guidance may be obtained from the supplier of the equipment.

  • Thank you for clearing it for me. Just a doubt. The figure 110%, (5%+5%) you got in accordance with BS 7671 right?