Circuit Breaker Selection

Hi

I have to decide on a circuit breaker for a 22 KW, 3 phase 400V Air compressor. 
Load current = P / (1.732 * V *PF) =22000 /(1.732*400*0.8)
= 39.69A

Therefore a 40A Type D CB is used.

These are my questions:
1. Do we have to include the PF if not given in the equipment datasheet for current calculation.
2. Is this the right way to find the size of MCB? i will also be including an overload relay. Is there anything else i need to lookout for?

Thank you in advance for your help.

Parents
  • I am not aware of any SPECIFIC regulatory requirement to allow a 10% margin but would presume that this comes under accepted good practice/good design.

    It depends a bit on the nature of the load and reasonably expected use. For a load expected to be used continually throughout the working day I would allow a 10%margin as described.  For a load used only briefly I might not bother.