Hi, I've been asked to make units and install a panel with universal mains sockets. I don't believe these are safe to use. But the customer has sent me a British General version which purports  to be complaint with BS1363-2 and IEC60884-2.

Has anyone had any knowledge of these finger fiendish accessories?

Parents
  • The 827 I presume ?

    https://www.bgelectrical.uk/wiring-devices/moulded/round-pin-export-socket-outlets

    Not as liberal as some designs,  and shuttered. Looks not too bad at first glance.  Should always be behind a 16A or smaller breaker or fuse.

  • BS1363-2 6.1 the rated current of all socket-outlets shall be 13A

    Not that is a major issue but surely that prevents it being to BS1363?

    Also how does it work with US stuff?

  • The  kit with a  US  plug has to be universal voltage, or it goes bang. Luckily most laptops, phone chargers, shavers and so on are nowadays.

    In the past when I have fitted trick sockets I have also fitted a local fused spur style isolator, and nowadays it would be an RCD one, in a twin box along side.

      

    and labelled it very carefully as   ! Caution 230V !


    Note that this model does not actually cover the most likely visitor, the European where a 'schucko'

    would perhaps be more useful, and would actually earth properly. In these BG ones they fit and energise but do not connect to the earth - not a great situation.

    Mike

Reply
  • The  kit with a  US  plug has to be universal voltage, or it goes bang. Luckily most laptops, phone chargers, shavers and so on are nowadays.

    In the past when I have fitted trick sockets I have also fitted a local fused spur style isolator, and nowadays it would be an RCD one, in a twin box along side.

      

    and labelled it very carefully as   ! Caution 230V !


    Note that this model does not actually cover the most likely visitor, the European where a 'schucko'

    would perhaps be more useful, and would actually earth properly. In these BG ones they fit and energise but do not connect to the earth - not a great situation.

    Mike